Pauuly48
12-21-2007, 10:22 AM
I need help on diagnosing this unit it is a little over a year old and has had one compressor change. I am getting a vaccum and 175 on high side. amp draw on compressor is 4.8 rated 8 amps. lo side pipe temp is 66 and high side entering condenser is 110 and exit is 72 I did evacuate this unit and I got oil in my hoses, recharged and got the same results. The compressors on theses units are famous for going out. The refrigerant is 404A compressor model is ACC MPT12CD model number on unit is KDC87.
I think I have a restiction or a bad compressor. Please help and advise as to what to do if it is a restriction?
Thanks Paul
markettech
12-21-2007, 05:24 PM
Which thread do you want us to post to Pauuly?
This One (http://hvac-talk.com/vbb/showthread.php?t=157256)
This One (http://hvac-talk.com/vbb/showthread.php?t=157249)
This One (http://hvac-talk.com/vbb/showthread.php?t=157248)
Or the one above..........I'm so confused:confused:
You may want to take a look at this (http://hvac-talk.com/vbb/showthread.php?t=1241).....paying close attention to rule #10;)
Pauuly48
12-24-2007, 03:00 PM
Which thread do you want us to post to Pauuly?
This One (http://hvac-talk.com/vbb/showthread.php?t=157256)
This One (http://hvac-talk.com/vbb/showthread.php?t=157249)
This One (http://hvac-talk.com/vbb/showthread.php?t=157248)
Or the one above..........I'm so confused:confused:
You may want to take a look at this (http://hvac-talk.com/vbb/showthread.php?t=1241).....paying close attention to rule #10;)
I did read the rule and thanks I didnt know that when I was told to move it I did and moved it to different places. I am sorry if this offended you and you have my humble appologies. Thanks paul
beenthere
12-24-2007, 03:16 PM
Did you use nitrogen when you changed out the comp.
Did you change out the cap tube strainer when you did the comp.
At 175 head pressure, and liquid line temp of 72, you only have 8* subcool.
Shut it down and see if the pressures equalize. If so your scale could be off.
Pauuly48
12-24-2007, 03:36 PM
I did not change the compressor, I will clear out lines then replace the filter drier evacuate and recharge I will use nitrogen both to clear lines, solder and pressure check for leaks. If you have anything else I should do before I recharge this sytem I would greatly appreciate any advice! Thanks Paul
markettech
12-24-2007, 03:37 PM
I did read the rule and thanks I didnt know that when I was told to move it I did and moved it to different places. I am sorry if this offended you and you have my humble appologies. Thanks paul
Offended me? Nah, it would take a little more than that to offend me (not much more though.......:D).
Confused was more like it...........it was like deja vu and it was freakin' me out:eek:....:D
beenthere
12-24-2007, 03:40 PM
Check your scale to see if its acturate at measuring ozs.
It could be telling you that you put in 12ozs. when you only have 9ozs in.
Pauuly48
12-24-2007, 03:49 PM
Check your scale to see if its acturate at measuring ozs.
It could be telling you that you put in 12ozs. when you only have 9ozs in.
Okay I will do that I do have a computerized scale i will check calibration.
Pauuly48
12-24-2007, 03:56 PM
Okay I checked my scale it is right on.
beenthere
12-24-2007, 06:06 PM
Blow out the evap and cap strainer.
Pauuly48
12-27-2007, 11:45 AM
Blow out the evap and cap strainer.
Thanks for all your help this unit is running good now!! paul
beenthere
12-27-2007, 05:09 PM
No problem.