Does anyone know of a source of preprinted maintenance sheets that would carry all the normal pm work done on hvac? Something that would have a checklist or fill in area's for work performed.
ryan_the_furnace_guy
07-31-2007, 08:24 AM
Most of them are bought and paid for, I may be wrong, but company owners probably won't share them for free. However, it is my opinion that you should thoughtfully and carefully design your own maintenance sheets. I don't personally like the ones used by my company.
Here is a basic summary of what I would do...
Furnace:
RUN A FULL TEST CYCLE
clean flame sensor
change thermocouple
clean electrodes
clean pilot
clean burners
flush drains
clean condensate trap
clean combustion chamber
clean cabinet
clean blower/inducer motor cooling vents
check blower for proper amperage, balance, rotation
check inducer for proper amperage, balance, rotation
oil any motor bearings (if applicable)
would not include a blower motor pull/clean (with proper filtration this shouldn't ever be needed and it takes too long to do for a small maintenance charge)
open humidifier bypass damper (if applicable)
check air filter
check humidifier media
check uv bulbs
check vent pressure safety
check limit/overtemp safety
check pilot/flameout safety
inspect heat exchanger
check temperature rise
check zone motors (if applicable, although you may want to charge an add-on for this)
inspect air intake a furnace for debris (may want to inspect vent terminations outside - if applicable - for plant overgrowth, dog fur, other foreign objects that should not be there)
perform a CO inspection of home
talk about customer comfort/IAQ concerns
AC:
RUN A FULL TEST CYCLE
check delta-T across evaporator
flush drains
clean condensor coil
clean evaporator drain pan (if cased coil and accessible)
would not include an evaporator coil cleaning as this is time-consuming and should not be needed with proper air filtration, however, maybe a spray-down with a special detergent, but not removing end blanks and cleaning the fins, just my opinion
test amperage of condenser fan and compressor
look at condition of contacts on the contactor
look for signs of trouble (swelling, oil leakage) from the capacitor
make sure all wires are properly suspended where they won't likely get cut/damaged by weed whips, etc
make sure ground lug and all electrical connections are tight and clean
check/record refrigerant operating pressures after 10 minutes of runtime
check/record necessary temperatures for superheat/subcooling readings
make gage port caps and service valve caps are tight
close humidifier bypass damper (if applicable)
check air filter, humidifier media, uv lights
check zone motors (if applicable, although you may want to charge an add-on for this)
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.