rogerraw
07-18-2007, 03:02 PM
I have a 5 ton Carrier Heat Pump installed in AZ. The outside temp is 110. The pressures on the unit read 300 high side and 80 low side. However the vapor line is barely cool and the compressor overheats and shuts down and then restarts. Is it possibly an obstruction in the TXV? Or do you have any other suggestions.

skippedover
07-18-2007, 03:04 PM
Not nearly enough info to troubleshoot over a website. Call a local pro in pronto. :D

makinmoney
07-18-2007, 03:12 PM
Not nearly enough info to troubleshoot over a website. Call a local pro in pronto. :D

I concur.....it could be many different things, Need much info.

shodinjido
07-18-2007, 03:29 PM
Definitely not enough info to troubleshoot.
Although, I doubt it is a restriction in the indoor TXV (if there is one)...suction pressure is too high. Most likely something in the condenser bypassing.

Roscoe
07-18-2007, 04:03 PM
I have a 5 ton Carrier Heat Pump installed in AZ. The outside temp is 110. The pressures on the unit read 300 high side and 80 low side. However the vapor line is barely cool and the compressor overheats and shuts down and then restarts. Is it possibly an obstruction in the TXV? Or do you have any other suggestions.


Hey you got that far, pressures, temps.........hell just fix it ...:rolleyes: .

....or call somone who can.......................;)

OR here ya go............


Definitely not enough info to troubleshoot.
Although, I doubt it is a restriction in the indoor TXV (if there is one)...suction pressure is too high. Most likely something in the condenser bypassing.

AtticAce
07-18-2007, 09:51 PM
Pressure clean the outside coil, and see what happens. After that I need some more info. In my area of the country it could be quite a few other things, to include a previous service call by Blow and Go Inc.

Advanced Response
07-19-2007, 05:18 PM
Pressure clean the outside coil? ROFLMFAO

After doing that give your local hvac company a call and have a new unit installed!!

Wow some of the answers around here lately..
Goodluck
J

Roscoe
07-19-2007, 05:23 PM
Pressure clean the outside coil? ROFLMFAO

After doing that give your local hvac company a call and have a new unit installed!!

Wow some of the answers around here lately..
Goodluck
J

hehehe what?...................... you didn't like that....... I find it pure amusement ..:D............. just as you did........ROFLMFAO

The Penguin
07-19-2007, 07:18 PM
giddyup :D

nhonhang
07-19-2007, 09:31 PM
I have a 5 ton Carrier Heat Pump installed in AZ. The outside temp is 110. The pressures on the unit read 300 high side and 80 low side. However the vapor line is barely cool and the compressor overheats and shuts down and then restarts. Is it possibly an obstruction in the TXV? Or do you have any other suggestions.

Your system was over charge

Kevin Weaver
07-19-2007, 10:56 PM
is this a puron unit? if it is its low on charge. If its r-22, then feel the little freon line. if its hot, clean outdoor coil. 80 psi suction is not out of line if its stinken' hot inside. really need more info. though