06-19-2007, 11:16 PM
Problems are: Carrier 30gxr135 ver. 4
Unit trips on low suction saturation temp circuit A
circuit B looks good. 2 deg aproch and 7 deg delta T
Pretty sure its not low gas.
suction pressure hunts from 35-60 psig
discharge superheat goes from 1 deg to 35 deg and sat suct. temp also varies
Went through ext tests, all looks good
unloaders are not energized at this time. I know it sounds like they are.
I'm thinking float in the economizer sticking ??
Any good ideas.
Thanks Union boy