View Full Version : Temperature difference between return and vents
dsanders55
06-18-2007, 09:02 AM
My temperature difference from the return and the registers vary. On cool days (and night) I get a 16 to 20 degree difference. During the middle of the day, the temperature difference drops to around 10 degrees (78 at the return and 68 at the registers). I'm hoping it could be as simple as a leak in the ducts coming from the return. These are in the attic where it would be cooler in the evenings and HOT during the day. Could something else cause this problem?:confused:
Shophound
06-18-2007, 09:20 AM
Duct leakage is a possible cause, particularly on the return side.
Also, old, torn, or missing duct insulation can also cause you to lose capacity from your system via attic heat gain to the duct supply air. If you have the old gray jacketed flex duct, and it's been up there for some time, it's possibly falling apart. Over time the jacket deteriorates in the intense attic heat, exposing the insulation and duct liner underneath, which over time causes it to break down, and you start getting leaks.
dsanders55
06-25-2007, 07:53 AM
I had the ductwork checked and he found no leaks. He suggested that our heat pump was too small. We have a 1 story ranch with about 2400 sq ft. Our heat pump is 3 ton. He recommends 1 ton for every 600 sq ft. Is this right?
I had the ductwork checked and he found no leaks. He suggested that our heat pump was too small. We have a 1 story ranch with about 2400 sq ft. Our heat pump is 3 ton. He recommends 1 ton for every 600 sq ft. Is this right?
Did this system ever cool the house properly?
Oftne hard to find return duct leaks,maybe they missed some.
The temp drop changing is not an indication of the system being undersized.Sounds more like duct leakage,or poor duct insulation.
Tons per square foot is a "Rule of Thumb/Dumb.
A Manual J load calc is what is required,call around asking until you find someone that will do one.
skippedover
06-25-2007, 10:31 AM
A Manual J load calc is what is required,call around asking until you find someone that will do one.
Why is a manual 'J' important? Well, if you measured the square footage of your home, as you did apparently, you got 2400. Using the techs formula for tonnage, you need a 4-ton system. Okay, now let's take the roof off you house. It's still 2400 square feet but you're trying to heat or cool the entire world. How big a system do you need now? A Manual 'J' calculation will reveal that information. What about a skylight in a room, high ceilings, picture windows, windows of equal size and construction that face different sun exposures? Manual 'J' takes it all into consideration. Accurate, repeatable results are where it's at.