Ok i got a ycas0100 chiller with the high psi switch broke off. I was wondering what hp switch was on the compressor? Whats the cut out and the cut in?
heatingman
06-08-2007, 06:02 PM
Most likely cut out, w/ cut in at a lower pressure on same switch. EXAMPLE cut out 150 reset at 125.
michael26
06-08-2007, 07:36 PM
ycas is a york screw. high pressure cutout should be about 400 and relief opens at 450. you could check the manual it will be in there or give york a call.i am pretty sure it is 400 closes at maybe 325.
fordtrucksrule
06-08-2007, 08:50 PM
Yep well i figured it out it cuts out at 405 and cuts in at 305 thanks for your guys reply.