I tried my ac a couple of weeks back and it worked for a while then stopped. I started poking around in furnace with a volt/ohm meter and found no voltage coming from transformer. Replaced the transformer, now blower will work, funace will work but no ac.
Switched to ac the transformer started heating up (which is probably what fried the old one). I could hear relay switch w/coil humming so I removed relay to replace. after taking out relay I jumped 24v to relay off transformer and it switched contact points like it should. Then I checked the 2 leads that run to relay and they only showed 7.3 volts could this be a problem with stat or possibly the control board? Any suggestions would be greatly appreiated!
cooling & heating confused
Switched to ac the transformer started heating up (which is probably what fried the old one). I could hear relay switch w/coil humming so I removed relay to replace. after taking out relay I jumped 24v to relay off transformer and it switched contact points like it should. Then I checked the 2 leads that run to relay and they only showed 7.3 volts could this be a problem with stat or possibly the control board? Any suggestions would be greatly appreiated!