frostmonkey
03-06-2007, 08:33 PM
Hey Guys ran across an unusual situation today. Meat manager complained of several sections of his fresh meat cases warm. When I arrived at the store I found a total of 8 3 ft sections warm spread out through 16 cases ( Each case has 3 seperate coils). Checked subCooling at the inlet of the TXVS to find it at 15 Deg F,checked Superheat to find it at 25-30 Deg F. A small adjustment of the valve(1/8 to 1/4 turn open) would cause the valve to open and begin to feed. I'm thinking its caused by wax in the seat, mainly because there has been a history of pluged valves in this store since it was built 5 years ago. The rack that these cases are tied into is refurbished, so I suspect I will be experiencing this problem more in the upcomoing weeks. Anyone have any suggestions on how I can clean up this wax? And has anyone ever experienced waxing of this magnitude. This is a R-22 rack,with Zerol 200td oil.:confused: