rommel21
03-01-2007, 06:58 PM
lierbert challenger 2, will not shut off compressor on pump down, perform pump down test,o.k.still runs. disconected all wires to low pressure switch. still runs.contactor not stuck closed.24 volts still to contactor coil. noticed on print ,paralel circuit ,in the board itself to k1 relay. anyone ever have a problem with board relays sticking close. the print decription calls it a positive start relay.
HVACJOEK
03-01-2007, 07:53 PM
Which level control??? More then likely you will find a jumper on the triac pull it and see if it resolves your problem. :cool:
rommel21
03-01-2007, 08:52 PM
hvacjoek, the jumper was not pluged it to any of the test pins . going back tommorrow to check seperate problem on the conderser. i will plug in test jumper on cool to see if it might bump the k1 to relay to stay open .
HVACJOEK
03-01-2007, 08:56 PM
Could be a bad board... I have seen hundreds of them when i was a liebert rep...rule out anything external to the board before you condemn it..:cool:
Airmechanical
03-02-2007, 08:21 AM
yes i have had exact same problem, call tech support they will tell you
which capacitor to cut off the board, i know it sounds weird, but they will
know about that problem!
.
HVACJOEK
03-02-2007, 05:18 PM
That is correct a few years ago there were some bad boards that gave nuisance alarms and the fix was to cut out the capacitors, have the number of the board handy when you call , it only applies to a certain series of pc boards...but also a low control voltage can also cause problems like you have. The capacitor thing applies to later version controlers then the ones you can put a jumper on. :cool: