View Full Version : Cool fail
joken
02-05-2007, 06:04 PM
It's easier to ask than hunt for the manual. What initiates the "Cool Fail" on the display of a Voyager Heat Pump's digital stat. Thanks, Ken
chillerout1
02-05-2007, 07:10 PM
call for cool and discharge air temp did not drop
jayguy
02-05-2007, 10:02 PM
cool fail:
1. Cooling and/or heating set point (slide pots) on ZSM have failed.
2. Zone temperature thermistor ZTEMP on ZSM failed.
3. CC1 or CC2 24 VAC control circuit has opened.
4. CPR1 or CPR2 DISABLE circuit (LPC) opened, during 3 minute minimum ON time, on 4 consecutive compressor starts.
5. Open circuit on programmable sensor terminal 12 at LTB.
jayguy
02-05-2007, 10:11 PM
sorry, i missed the whole digital tstat thing.
if it only displays "COOL FAIL" then: No communication between terminals 11 and 12. Verify changing voltage.
hvacowboy
02-05-2007, 10:37 PM
Does it have microcontrols or reliatel?
weathered-tron
02-06-2007, 09:39 PM
most common problem for cool fail is LPC opening due to refrigerant circuit problem or defective LPC. verify circuit through LPC proper open and close pressures. test while system in heat, defrost & cool mode
just_opinion
02-07-2007, 05:06 PM
Because it is a piece of junk Trane. I can wire a lock-out relay and it does the same ting as that piece of junk called Reliatel board. Enough bassing the brand - SORRY
Cool failed cause by:
Low pressure switch open 4 times with one call of cool.
Open coil or shorted coil of the contactor.
High pressure open one time.
They are all automatic reset. So take your pick.
My recommend is to check you double pole relay that energizes your outdoor fan. Either the board forget to send the 24 volt out or its point are not made.
Good luck
Can't stop the TRANE. If they cannot spell the word TRAIN, how can they design the unit. My bad again
supertek65
02-11-2007, 04:36 PM
Does it have microcontrols or reliatel?
where have you been Brad?
red bird hunting!
twisted pair
02-13-2007, 06:14 PM
Trane is not the only one who does not know how to spell!!!!!!!!!!!
supertek65
02-13-2007, 06:24 PM
Trane is not the only one who does not know how to spell!!!!!!!!!!!
TING BASSING
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.