View Full Version : ruud upflow ugph-07eauer



Chuck Nantz
02-03-2007, 01:34 PM
I am having problems with a ruud furnace the customer says it is intermittent. When it is "broke" nothing happens. No draft motor nothing. He says when u "wiggle" the purple wire on the pressure switch it starts and does fine. Of course i am never there when it is "broke". Everything checks ok when i am there. The switch has 24 or so volts at both sides and the wires at the bulk head have the right voltage. I have inspected the wires and nothing looks like it would have a short but.....

BaldLoonie
02-03-2007, 03:34 PM
Rheem/Ruud bought some cheap plastic pressure switches a few years ago. They like to stick stuck. Wiggle the sucker and she'll open allowing the inducer to come on and then they'll close. Needs to be replaced.

Chuck Nantz
02-03-2007, 08:30 PM
Thanks alot for the info.