PDA

View Full Version : charging a heat pump



downsouthjunkin
02-03-2007, 01:33 PM
what's the best way to charge a heat pump in heat mode w/ an ambient temperature of 30-40 degrees?

smokin68
02-03-2007, 04:14 PM
what's the best way to charge a heat pump in heat mode w/ an ambient temperature of 30-40 degrees?


Hire a professional to do it.

davefr
02-03-2007, 05:22 PM
what's the best way to charge a heat pump in heat mode w/ an ambient temperature of 30-40 degrees?

1. Recover and weigh back in based on system capacity and correction chart for line set differences. (preferred)

OR

2. Refer to the manufacturers chart and re-adjust come cooling season

You need EPA 608 Type II license to do this.

iwannahelp
02-03-2007, 05:26 PM
You can charge a heatpump with VISA, Mastercard, Discover, Amer. EX, or pretty much any other major credit card when you call a pro to do it for you.

downsouthjunkin
02-03-2007, 05:41 PM
1. Recover and weigh back in based on system capacity and correction chart for line set differences.
2. Refer to the manufacturers chart and re-adjust come cooling season

You need EPA 608 Type II license to do this.

Got the license,not a novice.Just asking!!!Currently a Quality technician for a HVAC manufacturer.Thanks!