fridg
02-02-2007, 05:02 PM
Had a few small hermetic compressors on freezer cabinets that make a strange pumping sound.
(like on a fly spray can when you press the nozzle down then let go then press again)
It only makes this sound for the first 10 seconds after an off cycle , and even when the cabinet has been turned off for 24 hrs.
Monitored suction pressure and it fluctuates up and down 100 kpa , amp draw fluctuates up and down with the suction pressure , and this is just for the first 10 seconds while the comp makes this noise. Head pressure is normal , cabinet pull down rate is normal.
After this time the unit runs fine , amps good , suction good , no noise.
This unit has a cpr fitted , and adjusted so it is not liquid , charge weighed in from nameplate.
The engineers and reps have come in to take it away , for an explanation on why this occurring.
(like on a fly spray can when you press the nozzle down then let go then press again)
It only makes this sound for the first 10 seconds after an off cycle , and even when the cabinet has been turned off for 24 hrs.
Monitored suction pressure and it fluctuates up and down 100 kpa , amp draw fluctuates up and down with the suction pressure , and this is just for the first 10 seconds while the comp makes this noise. Head pressure is normal , cabinet pull down rate is normal.
After this time the unit runs fine , amps good , suction good , no noise.
This unit has a cpr fitted , and adjusted so it is not liquid , charge weighed in from nameplate.
The engineers and reps have come in to take it away , for an explanation on why this occurring.