ddcctrl
02-02-2007, 12:54 PM
Wanting to use Aux contact on T730H1009 for time-of-day control of extra equipment. Anyone know which nvi to use to enable/disable contact? Tridium R2 JACE, T7350Cs shadow object.
codewriter
02-02-2007, 04:54 PM
If your talking about actually controlling that contact via a nvi, your not going to be able to. You can setup what the aux contact does with the Config_auxOpMode, but no way to manually control it from the network.
Use a LONRIB, that will probably be the most cost effective thing to do, and you can use the loads power to power the LONRIB, so no extra power wiring needed, just the LON cable ran to it.
amigo
02-02-2007, 04:58 PM
Or use a viconics stat (if in design phase) which has network commadable contacts.