hI everyone
i just recently got into the field of commercial hvac.
i'm having trouble with these trane rtu with reliatel, it's control by a trane thermostat with a sensor next to it.
my first question, is the unit control by DC voltage? because the terminals R W G Y aren't being use.
second what type of sensor was it, that was mounted next to the thermostat?

jayguy
02-02-2007, 12:46 AM
do you have any model numbers off of the tstat and unit? the reliatel can have either a "trane" tstat, which is communicating, or a standard tstat (R, Y, G, etc), or trane bas.

TomTom Cool Man
02-02-2007, 09:23 AM
What Is Being Used 6 7 8 9 10 11 12 14 Our What.give Us More Info,thanks Tomtom Cool Man

svc
02-02-2007, 11:50 AM
baysenso19b or c ,yes it is dc voltage. awesome thermostats. As far as the "sensor" are you sure it is part of the hvac controls? if so maybe a remote smoke detector module? need more info?

amickracing
02-02-2007, 12:15 PM
They work well until they don't work... then I swear it's voo-doo that runs them units!

Check this stuff out too, might help you along the way.
http://www.hvac.amickracing.com/RTU Training/Trane RTU info/ (http://www.hvac.amickracing.com/RTU%20Training/Trane%20RTU%20info/)

deon1116
02-02-2007, 04:38 PM
What Is Being Used 6 7 8 9 10 11 12 14 Our What.give Us More Info,thanks Tomtom Cool Man

yes it was hook up to the 6 7 8 9 10 11 12 14 terminal?
can anybody tell me how does it work.

iwannahelp
02-02-2007, 04:57 PM
they have low DC voltage on the numbered terminals. NEVER jumper any two termianls together or you could be in for a world of poo. I always test operation by jumping the test pins repeatedly to get to the function I want to turn on. If ya read the service man. unitary processor control it can tell ya more in detail.

ej45
02-02-2007, 08:31 PM
They are very easy to troubleshoot once you get your hands on the reliatel book. Link is in post above. From the terminals you read your DC volts to get information. For example..........If you came up to the unit on a no cooling call and fan running and compressors off. Check DC voltage at terminals on RTRM board at 6 and 8. If you read around 30 volts, its a call for cooling, If you read .75 volts, no call for cooling, If the voltage is blinking or spiking from 30VDC to 15VDC (not steady), thats a cool fail.

The heat works the same way on teerminals 6 and 7.

All this is in the book..

The other nice thing is if your on the roof you can measure the voltage at the terminal board and see what mode your in from the tstat. This is nice for fan ON or AUTO and heat, cool, auto.

Terminal 1 is zone temp
Terminal 2 is common to sensor
Terminal 3 cooling setpoint
Terminal 4 mode
Terminal 5 heat setpoint

Terminals 7 thru 14 are for programmable sensor like you have

All this unit needs to operate in a jam is a senor on 1 and 2 and the unit will run fan ON and maintain 74 cool and 71 heat on its own.

Get reliatel book RT-SVD03D-EN
Get Voyager book PUB No. 22-7706-06

You cant troubleshoot these with out the book till you get on to them.

ej45
02-02-2007, 08:48 PM
I wanted to share more information with you about the reliatel control system.

Every module in the system works on a comm bus between the boards. You can ID the bus by looking for the four wires and typically a twisted pair. This is your 24 VAC, 24 com, Comm twisted pair. You can find them on all the boards. Look at the RTRM board and find the J4 plug. Thats the BUS.

This bus or comm wires will connect all boards like the ignition, economizer, options, ect.....

Voodoo problems or abnormal operation can be traced from boards by disconnecting board one at a time and resetting power and rechecking operation. (disconnect board by just comm wire plug)

After any changes in bus circuit or zone sensor, cycle power and on start up the reliatel system self checks itself and looks to see whats on the bus and what kind of zone sensor or conventional stat is hooked up.

Trane has had its share of problems with the economizer module (ECM) that has done some unexplained problems. If I suspect this, I unplug the Comm plug on the ECM and then recheck.

I hope this helps.

ej45
02-02-2007, 08:59 PM
yes it was hook up to the 6 7 8 9 10 11 12 14 terminal?
can anybody tell me how does it work.

7 is heat status
8 is cool status
9 is system status
10 is clogged filter or fan fail
11 common
12 comm comunication
14 24 VAC

This zone sensor is like another module in the system, the terminals 11,12, and 14 are the bus and all that is needed to operate the RTU. All the information/communication is thru these three wires. The other 7 thru 10 are status outputs from the RTU to the zone sensor. If the RTU heat locks out because of a failure, the programmable zone sensor will show HEAT FAIL on the display on the 7 terminal. (blinking)

I hope this helps.

ej45
02-02-2007, 09:06 PM
Just another tip for you all

A heat fail on a Voyager with a UCP board = a limit in the return section opened. If the ignition control locks out this will not produce a heat fail.

On Voyager 3 units VAV in the test mode for heat, when you test out wait for 6-7 minutes before the heat will turn on. this allows time for the boxes to drive to 100% open. This could drive a guy nuts the first time you run into it.

ej45
02-02-2007, 09:44 PM
erikbaer45acp@yahoo.com

Send me an email and I will try to send you the PDF files for the information you need.

esornivram
02-02-2007, 11:27 PM
untill they start stopping up the freon driers
of start blowing out compressor terminal boxes, shorting to ground
I have seen ice build up on the short header orifices used for expansion device
all compressor should have CCH heaters on them and anytime you find failed CCH's or the non install of them, get the wiring harness for them and put them on,
http://hvac-talk.com/vbb/showthread.php?t=117398
http://hvac-talk.com/vbb/showthread.php?t=115384

gerizam60
02-07-2007, 10:32 PM
HI,

you can go to Trane's web site and look under Literature and have a picnic. Lots of valuable info, and printable in .pdf format.

Also, all Trane service manuals should be available in a pocket glued to the electrical access door. This IS basically the same info you'll find on Trane's website.

If it's not there, and the RTU is part of a service contract within your co., you should replace it with a new copy for the next guy.

Here's a direct link for you, so dig in. http://trane.com/commercial/equipment/SearchResults.aspx

Check out the book store too, Lots of self training material.

aixha1969
04-09-2013, 09:52 PM
Great information.

ACFIXR
04-09-2013, 10:19 PM
hI everyone
i just recently got into the field of commercial hvac.
i'm having trouble with these trane rtu with reliatel, it's control by a trane thermostat with a sensor next to it.
my first question, is the unit control by DC voltage? because the terminals R W G Y aren't being use.
second what type of sensor was it, that was mounted next to the thermostat?

Tip-

Be careful when trying to reach the pressure switch's molex connectors on some of the smaller units.

372791

The back of your sweaty hand might come across the line terminals on the back of the transformer..............:whistle:

jpsmith1cm
04-10-2013, 05:47 AM
moved to tech to tech chat

r404a
04-10-2013, 08:41 PM
erikbaer45acp@yahoo.com

Send me an email and I will try to send you the PDF files for the information you need.

great info ej45 thanks for the posts