View Full Version : Heat Pump Ice Up



condojack
02-01-2007, 04:41 PM
Have a Lennox heat pump that ices up on me. Have replaced defrost board & checked out refg charge. There does not seem to be a sensor connected to board, and the wiring diagram is un-readable. Fan speed is OK, reversing valve is OK. Can not get it to go into defrost cycle by itself. Need advise & a wiring diagrtam for Lennox HP HP22-411-3P. Also does anyone know what manufacter handles parts for Air Pro heat pump, can not find any in my area.

iwannahelp
02-01-2007, 04:49 PM
It has a defrost thermostat. It has two, one is for defrost(which is the one you want) and the other is for discharge temp. of compressor(don't mess with that one). Really can't go into much detail since I don't think it is allowed on here, but I know for a fact that is does have a thermostat.

condojack
02-01-2007, 05:06 PM
Thanks iwannahelp I will check that out, I wish I had wiring diagram.

davefr
02-01-2007, 05:26 PM
Thanks iwannahelp I will check that out, I wish I had wiring diagram.

Have you tried searching? Lennox makes some of their technical installation manuals public. Go to the installation manual section vs the owners manual section.

http://www.lennox.com/owners/archived-docs.asp

condojack
02-01-2007, 06:34 PM
Thanks Davefr for the info, will give them a try.

Msully
02-01-2007, 11:39 PM
As I recall on this unit it is strictly time based defrost. Defrosts according to jumper setting and terminates on thermostat.

condojack
02-02-2007, 01:34 PM
MSully thanks for the imput, will put it to good use.