I have a new Rheem modulating furnace that was recently installed along with the new touchscreen modulating t-stat (model HC-TST401MDMS). While I love the furnace, I am unhappy with the White-Rogers modified t-stat.
Yes, it looks cool and is easy to use. But the accuracy of the temperature readings of this unit is appalling.
While the furnace is in recovery mode, the t-stat temperature seems somewhat accurate as the temperature in the house rises. But once it starts getting near the setpoint, the temperature on the display will stop increasing and linger at the same value for a very long time.
While the t-stat temperature reading stays on the same value seemingly forever, every other thermometer nearby will continue increasing. Once the temperature starts to stabilize, the Rheem t-stat will consistently read 2 to 3 degrees cooler than all the other thermometers.
This appears to be a common problem with this unit. If you review each of these threads below, you'll see others that complain about the temperature reading "3 degrees too cold".
http://www.hvac-talk.com/vbb/showthread.php?threadid=118952
http://www.contractortalk.com/showthread.php?t=15861
http://www.hvac-talk.com/vbb/showthread.php?threadid=120940
In an attempt to remedy the problem, I went into the "installer menu" on the t-stat and set a +2 degF temperature offset. Doing this gave me a reasonably accurate temperature near setpoint.
HOWEVER, I discovered that placing a +2 degF or greater offset into the t-stat will effectively disable the modulating function entirely! I discovered that whenever a large offset is in place, the furnace fires at 100% continually!
It appears like this may be a firmware bug in the t-stat. It is as if the algorithm for determining how far to open the valve is not properly taking into account the temperature offset. i.e. the t-stat likely thinks it is ALWAYS at least 2 degrees or more away from setpoint, so it fires at 100%.
Interestingly, the heat-on & heat-off signaling in the t-stat does appear to apply the temperature offset correctly. It is as if the Rheem modifications for determing the valve setting do not work right with non-zero offsets, but the original White-Rogers logic for everything else does.
I have discussed this with my dealer, who has in turned discussed the issue with Rheem. Rheem says it shouldn't be behaving like this, so they are going to give me a new t-stat. But honestly, I am not confident this will fix the problems unless they actually send a t-stat with a new version number. (My current t-stat says "Rev A" on it.)
I know I am not alone in these problems based on the seemingly identical complaints I've read on various HVAC message boards. Anybody have any thoughts or additional info on this matter?
Yes, it looks cool and is easy to use. But the accuracy of the temperature readings of this unit is appalling.
While the furnace is in recovery mode, the t-stat temperature seems somewhat accurate as the temperature in the house rises. But once it starts getting near the setpoint, the temperature on the display will stop increasing and linger at the same value for a very long time.
While the t-stat temperature reading stays on the same value seemingly forever, every other thermometer nearby will continue increasing. Once the temperature starts to stabilize, the Rheem t-stat will consistently read 2 to 3 degrees cooler than all the other thermometers.
This appears to be a common problem with this unit. If you review each of these threads below, you'll see others that complain about the temperature reading "3 degrees too cold".
http://www.hvac-talk.com/vbb/showthread.php?threadid=118952
http://www.contractortalk.com/showthread.php?t=15861
http://www.hvac-talk.com/vbb/showthread.php?threadid=120940
In an attempt to remedy the problem, I went into the "installer menu" on the t-stat and set a +2 degF temperature offset. Doing this gave me a reasonably accurate temperature near setpoint.
HOWEVER, I discovered that placing a +2 degF or greater offset into the t-stat will effectively disable the modulating function entirely! I discovered that whenever a large offset is in place, the furnace fires at 100% continually!
It appears like this may be a firmware bug in the t-stat. It is as if the algorithm for determining how far to open the valve is not properly taking into account the temperature offset. i.e. the t-stat likely thinks it is ALWAYS at least 2 degrees or more away from setpoint, so it fires at 100%.
Interestingly, the heat-on & heat-off signaling in the t-stat does appear to apply the temperature offset correctly. It is as if the Rheem modifications for determing the valve setting do not work right with non-zero offsets, but the original White-Rogers logic for everything else does.
I have discussed this with my dealer, who has in turned discussed the issue with Rheem. Rheem says it shouldn't be behaving like this, so they are going to give me a new t-stat. But honestly, I am not confident this will fix the problems unless they actually send a t-stat with a new version number. (My current t-stat says "Rev A" on it.)
I know I am not alone in these problems based on the seemingly identical complaints I've read on various HVAC message boards. Anybody have any thoughts or additional info on this matter?