View Full Version : York BP150 Package Heat Pump control Problem



flynfix
01-27-2007, 10:46 AM
York BP150C00N2AAA3 with no heat.
The book was not kept in the unit and as I do not service many York HP's I am not familar with control board codes.
2Blinks
7 and 8 blinks are low temp at evap coil compressor lock out.
previous fault said 9 blinks electric heat limit trip.
I searched the unit for the limit switch. Only one found was klixon in electric heat panel - it tested good.
I assume the comp. lock outs are due to extreme low tempoerature outdoors.
I tried York site on net for control literature with no luck.
Can anyone point me to a website for tech. info on these controls.
The cotrol board part # is 031-01934-001.

Thanks for any help.:confused:

Airmechanical
01-28-2007, 11:35 AM
York BP150C00N2AAA3 with no heat.7 and 8 blinks are low temp at evap coil compressor lock out.previous fault said 9 blinks electric heat limit trip, i assume the comp. lock outs are due to extreme low temperature outdoors.I tried York site on net for control literature with no luck. Thanks for any help.:confused:

if it went out on high temp limit, then low evap temp,

that would lead me to believe you have an air flow problem!



.