PDA

View Full Version : location of liquid drier



dknytech
01-24-2007, 05:24 AM
as for 1 hp ductless air-con outdoor unit, after a compressor replacement after burnout, where shall I put the liquid line drier, somewhere in between condenser and capillary tube or after capillary tube ?

mdharris68
01-24-2007, 06:08 AM
Liquid line filters go before the metering device.

EarthLoop
01-24-2007, 07:33 AM
Some ductless systems are not supposed to have a filter drier.. You should check with the manufacturer about it for your specific unit. We have already installed filter driers for 1 day after a compressor change out and then removed them.

dknytech
01-24-2007, 11:38 AM
actually which one is more suitable for the cleaning work after compressor burnout? liquid line or suction line drier ? or even both ?

EarthLoop
01-24-2007, 12:48 PM
actually which one is more suitable for the cleaning work after compressor burnout? liquid line or suction line drier ? or even both ?


we do both liquid and suction along with a R-11 flush....
then remove both filters after a day.

Mr Bill
01-24-2007, 01:07 PM
And a good long vacuum probably would probably not hurt much either. :D

EarthLoop
01-24-2007, 02:19 PM
And a good long vacuum probably would probably not hurt much either. :D

yes i totally agree.. anything over 400microns is unacceptable.