View Full Version : This call has me confused!
Gerbs1983
02-02-2013, 11:41 PM
One of our guys performed pm on a two system house, got a call a day later that the second floor system wasn't working/keeping up. He worked on it for a while, I was told to go see if I could figure it out. Here are the details:
Call for heat, inducer kicks on, pulls 1.97" wc, ps needs 1.35 to close. Ps closes, ignitor heats up. Gv energized, opens for less than a second and closes. Not open long enough for the flame to flow acrossed all four burners, literally less than a second and the gv is de-energized by the board.
Call for heat does not drop out.
Pressure switch does not drop out.
Inducer does not drop out, continues to pull 1.87 to 2" wc throughout the cycle.
No limits are opening to cause interruption.
Burners are clear all the way acrossed, flame sensor is clean (not on long enough for flame sensor to come into play at this point)
Here is the kicker, twice while trouble shooting the furnace lit and stayed lit. Once I shut it down and attempted to refire, problem reoccurred.
Have a new board installed at this time, same issue.
Furnace is a 94 Trane 90% upflow.
Any ideas/thoughts are greatly appreciated!
mark beiser
02-03-2013, 12:07 AM
Does it use the old radiant flame sensor system, or does it have a normal flame sensor rod?
billg
02-03-2013, 12:16 AM
Some times things happen faster than your meter can respond. Did you jump out pressure switch or thermostat? Also check wiring and gas pressure when valve is powered. At least it happens enough for you to see it.
Helioson
02-03-2013, 12:16 AM
Check your ground. A simple test is to make a "test" 12g ground wire from the board to a "good" known ground. It doesn't take long, is cheap and if it doesn't work you can at least cross it off your list. Good luck
suBcools
02-03-2013, 12:36 AM
The few times I've had the gas valve being mysteriously de-energized it turned out to be the pressure switch dropping out faster than my meter would respond. For a split second.
ComfortablyNumb
02-03-2013, 01:00 AM
What piece of equipment are you working on?
Did you try to jumper the pressure switch? Do you continue to have 24v signal to the valve?
I had similar occurrence with an older Rheem 80%. Valve would open for a split second then close, occasionally staying open.
I'm calling a failing solenoid in your gas valve.
In past experience mentioned, I would measure ~20-22 volts when the valve would open for a split second, sometimes not open and measure ~15v, sometimes 24v and would hold and valve would stay open, but rarely and very intermittently.
Removed leads from solenoid and test, would measure 24v and hold consistently.
Replaced gas valve and batta bing.
And btw although those funky voltage readings did obviously tell me of a problem, they may jot be exactly entirely accurate, as like someone said above, can happen so fast your meter barely detects fluctuations.
timebuilder
02-03-2013, 08:05 AM
The ground jumper should generally be used between the burner closest to the flame sensor, and to the board ground. Aside from boards in modern equipment that sense the presences of the equipment grounding conductor that comes from the service panel, the ground between the burners and the board are all that the board cares about for flame sensing.
Yes, you can jump out the safeties one at a time, but I'd consider if another gas appliance is running when this one tries to fire, causing low inlet pressure. Or, a defective gas valve.
hvacrmedic
02-03-2013, 08:32 AM
You have a poor connection somewhere, track it down. Could be literally anywhere in the active circuits, both low and high voltage, including the premise wiring, breakers, etc.,. It's a process of elimination. Test jumpers should help. If you're not losing 24 volts to the valve, then it's the valve.
Snapperhead
02-03-2013, 08:51 AM
snug every wire nut , and every screw with a wire
spade connectors , take off , gently pinch tighter with pliers , put spades back on
Now keep your meter on the gas valve and fire it up ... see if you lose power to valve when it drops out
uniservice
02-03-2013, 09:04 AM
This is one of the times that an old analog meter will be better at checking the valve input than a digital.
Gerbs1983
02-03-2013, 09:07 AM
In response to all of the above advice:
Normal flame sensor rod.
I have jumped out the stat, but not the pressure switch - I will try that.
I understand that these things can happen faster than a meter may be able to respond, yet did not think to jumper out pressure switch. I did monitor inducer pressure, did not go low enough to affect ps, yet could be that my meter response time is too slow.
I am losing 24 volts to gas valve.
I will make sure that no other gas appliances are fired. Incoming gas pressure: 6.5. Unable to measure manifold gas pressure, drops out too quickly.
I will check all connections, ensure good ground, and jumper out limits one by one when I go back. Thanks for the advice so far!
ch4man
02-03-2013, 09:25 AM
do you get a fault code?
im thinking cold solder joint on the board or possibly in the gas valve internals.
sometimes the best tool for this is you... start wiggling wires. hw smartvalves have been known for poor internal connections a grabbing the harness and moving it around works on thoses.. can happen on the IFC at the point where the gas valve wires connect.
good luck
Cosmicmuffin
02-03-2013, 09:34 AM
I made up a "Test" 24 volt transformer. plug into 120volt.,two jumper wires with clips! works great to test gas valves etc.
catmanacman
02-03-2013, 07:29 PM
im thinking bad gas valve
ComfortablyNumb
02-03-2013, 10:57 PM
I'm still saying bad valve...
Or maybe a grounding issue.
Also just remembered - disconnect the power supply and check for voltage between neutral and ground. Shouldnt have more than 0.5vac if so you may have a neutral/grounding issue. It's put an end to me banging my head against the wall before... on a Trane 90% if I remember correctly. Read between 15-25v while also getting 95-105v hot to ground.
gravity
02-03-2013, 11:47 PM
i installed a new system and went to fire off heat. i had a wire that went to safety switch on pump that broke 24v from board. when the unit went to energize gas valve it would drop out. I had 24v the entire time.
Come to find out, the wire i ran to the pump safety switch had a break in the wire. When the gas valve went to energize it would drop everything out.
make sure all your connections are good and no broken wires. check resistance thru your switches.
hope this helps
Makinhole
02-04-2013, 12:19 AM
I too had a similar situation, found poor connection at the molex plug. Hard to find some times, try moving wires around and observing meters and listening while you pray. You will get it. Jump 24v to gas valve and make sure valve is good before investing time in searching for your problem. Good luck.
cjpwalker
02-04-2013, 01:00 AM
Sounds like bad gas valve. Temporarily jump out the pressure switch and try a call for heat. Make sure you do it at the right time in the ignition sequence our you will fault on "swtich stuck closed." If no change, try unplugging the gas valve, make a call for heat and listen to the relays on the board. If the gas valve relay clicks and holds for the full four or five second trial for ignition it's most likely a short in the valve.
Gerbs1983
02-06-2013, 10:40 PM
Follow up:
Went back, all indicators were bad gas valve. Removed old gas valve, before installing new valve I hooked up low voltage to it. It worked correctly, so I installed. Once installed, fired system and gas valve lost 24v in less than a second...still no error code.
Continued to troubleshoot, was preparing to try a different board when I suddenly got an open limit switch error. Traced to rollout switch...it was open, it hadn't been before. Replaced with new rollout, fired furnace...fired correctly.
Furnace ran for about 3 min, then tripped the new rollout. Checked temp in burner box, not sealed...upwards of 200 degrees...opened up coil...dime size holes in 3 cells.
The kicker was that the original rollout for some reason was allowing enough voltage to get by for the furnace to light, yet as soon as there was flame it would trip, but just fast enough to cause the board to remove voltage from gv, never giving a limit fault.
Very weird.
ComfortablyNumb
02-07-2013, 10:53 AM
Funny how things end up working out.... but didn't you bypass/jump the limits first? Way to figure it out though.
So what about your guy that performed the PM????? He didn't see the dime sized holes? This problem just started the day after? Ouch.
toocoolforschool
02-07-2013, 11:22 AM
Funny how things end up working out.... but didn't you bypass/jump the limits first? Way to figure it out though.
So what about your guy that performed the PM????? He didn't see the dime sized holes? This problem just started the day after? Ouch.
x2
Will6688
02-07-2013, 02:26 PM
I had same problem with 90% turned out to be not venting. water backing into vent pipe.
Gerbs1983
02-08-2013, 09:06 AM
Yes, sadly I assumed the heat x had been checked during pm, but not the case. I had not jumped out that limit, my fault there. I think an existing problem was aggravated when the pm was performed, because the bad limit had to be removed in order to remove the burners. Good learning experience though, both troubleshooting and learning to not assume the previous tech did everything correctly (check heat x).
ComfortablyNumb
02-08-2013, 11:53 AM
Yes, sadly I assumed the heat x had been checked during pm, but not the case. I had not jumped out that limit, my fault there. I think an existing problem was aggravated when the pm was performed, because the bad limit had to be removed in order to remove the burners. Good learning experience though, both troubleshooting and learning to not assume the previous tech did everything correctly (check heat x).
Yup assuming has left me scratching my head a time or two... and it always sucks explaining something like that to a homeowner, when your guy was there to assure operation and safety... and now they need a new furnace... hope that all goes well for you guys. I would say that if this were to happen at my company, the new install would be discounted for the trouble... hopefully you have an understanding client! Good luck!
hurtinhvac
02-08-2013, 01:30 PM
Wow. Here I was getting all cockey and raising my hand like Arnold Horshack (if you don't remember him, p*ss off ;) )
I'm a little intrigued by the "2nd transformer" trick in a puzzler like this to quickly and decisively rule out the gas valve. Though I would just use 36" jumpers off the board xfmr after removing R to prevent a cycle. If you hook up your manometer to GV manifold tap, jump the valve and watch the pressure for a five seconds or so; it should quickly confirm the condition of the valve itself, right??? You could keep the valve open as long as you dare since the system would not be cycling and flame rectification would not shut it down.
In cases where the voltage drops so quick your meter doesn't register - like pressure switches that drop in and out so fast they don't even cause an error.
I caught a rudd/rheem late last year, going behind a 30 year tech. Sideways in an attic crawl. GV was chattering and I can't remember why exactly, but I was having trouble deciding if it was the valve or if control voltage was dropping out. I believe in the end I decided that control voltage was on the valve long and steady enough for it to prove flame, so I went with the valve, put it on later in the day and tested fine. But I recall having misgivings until it was resolved.
So anyone else simply jump control voltage to the GV and watch manifold pressure as a quick and easy test? Thoughts?
Gerbs1983
02-08-2013, 03:18 PM
We actually did that on this one. Took 24 v from board to valve, fired gv and ran without issue. Allowed us to rule out any issue w gas valve. First time I have done this, it also allowed us to run furnace long enough to trip roll out for good, leading to the root issue.
hurtinhvac
02-08-2013, 05:38 PM
We actually did that on this one. Took 24 v from board to valve, fired gv and ran without issue. Allowed us to rule out any issue w gas valve. First time I have done this, it also allowed us to run furnace long enough to trip roll out for good, leading to the root issue.
How exactly? You cycled normally and added another 24v to the GV, in addition to the 24v it might already be getting?
Or did you remove the existing wires from the GV? If so, how was the circuit completed?
Gerbs1983
02-09-2013, 12:09 AM
Removed existing wires from gas valve. Used jumper from r and jumper from common. Once board gave call for gv, manually gave gv 24v from terminal block on board.
Not sure if this is a good thing or a bad thing, but it worked. Allowed us to rule out gv and find the real problem. Also able to determine gas pressure.
hurtinhvac
02-09-2013, 12:33 PM
Removed existing wires from gas valve. Used jumper from r and jumper from common. Once board gave call for gv, manually gave gv 24v from terminal block on board.
Not sure if this is a good thing or a bad thing, but it worked. Allowed us to rule out gv and find the real problem. Also able to determine gas pressure.
I guess it's fine if the GV relay and GV are on their own little circuit. I just grabbed the nearest Carrier schematic I have and it appears the pressure switch has a way back to common thru the CPU, so that unhooking the GV wires would not effect the rest of the cycle. I never bothered to notice whether most furnaces are likewise wired, always assumed all the safeties were wired in series with GV to shut it down if one opened.
Gerbs1983
02-09-2013, 01:55 PM
True, on this particular Trane, the board controlled gas valve on its own mini circuit, per the 12 pin plug.
ComfortService
02-09-2013, 02:39 PM
Great idea, disconnecting existing wiring on the valve and running a 24 and common off the low voltage coming in, basically bypassing the board control, then testing the opening of the valve by the outgoing pressure..Thanks!
davidj001
02-15-2013, 07:48 AM
This is one of the times that an old analog meter will be better at checking the valve input than a digital.
thats why my simpson is still on the truck and the guys i work with know to keep their hands off of it!!!
davidj001
02-15-2013, 07:51 AM
encountered a similar problem (on an l.p. gas system) and found it to be the second stage regulator locking up as soon as there was a slight drop in pressure,
ADillon
02-15-2013, 07:59 AM
could be bad solenoid coil in valve, weak transformer, voltage drop across pressure switch (check w/ volts not continuity), overloaded transformer (disconnect all peripherals and jump unit out at IFC)
ADillon
02-15-2013, 08:01 AM
If the PS is in series to the gas valve, then my money would be on a volt or 2 drop across that switch
northernh
02-16-2013, 01:33 AM
Check if it properly grounded,than check gv valve.
Jesjen829
02-17-2013, 08:53 AM
I'm still saying bad valve...
Or maybe a grounding issue.
Also just remembered - disconnect the power supply and check for voltage between neutral and ground. Shouldnt have more than 0.5vac if so you may have a neutral/grounding issue. It's put an end to me banging my head against the wall before... on a Trane 90% if I remember correctly. Read between 15-25v while also getting 95-105v hot to ground.
I've measured up to 10 volts to neutral in the past. I thought this was just feedback. Could this be a clue that there is a problem?
timebuilder
02-20-2013, 05:34 PM
If if you or anyone else has 10 volts between the neutral and the equipment grounding conductor, you've got some work to do there my friend.
uniservice
02-20-2013, 07:34 PM
X2
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.