View Full Version : furnace burner???



chrisevansac
01-24-2013, 04:21 AM
www.facebook.com/video/video.php?v=4717479186278&notif_t=video_processed[/video]

had this one last night. inlet pressure is 6.9 and outlet pressure is 3.45. i cleaned the burners but the only one dirty was the first one that is rolling back at start up. cleaned orifices. still has roll back at start up. i did notice when i was turning the furnace on and off to check it, that if i didnt let the inducer completely stop before turning it back on it wouldnt have roll out. what do yall think?

rchristie420
01-24-2013, 09:37 AM
did you inspect the heat exchanger?

Snapperhead
01-24-2013, 10:04 AM
did you clean the pilot orafice ?

its like the gas valve is opening too slow

can you swap burners around ??

toocoolforschool
01-24-2013, 10:17 AM
check the amp draw on inducer fan motor.

chrisevansac
01-24-2013, 02:48 PM
Amp draw was .9 name plate 1.7

GastecD
01-24-2013, 03:05 PM
That is strange, make sure to share the outcome. Never know when youll come across something like this

chrisevansac
01-24-2013, 04:42 PM
I do remember the valve took about 2 or 3seconds to get to 3.45. Is that normal or is it usually immediate

Snapperhead
01-24-2013, 04:54 PM
I believe I heard they do make valves that are slow openers , i dont know enough about them to tell you anything , but if one got installed into that furnace on accident , it will act similar to what you are seeing

If the pilot flame is Not big enough it could do that , or make a Whoosh sound

Some are a real pain to diagnose

gravity
01-24-2013, 07:32 PM
Delayed ignition. Check the runners on the burners. Make sure they are spaced enough. Was the valve replaced?

gravity
01-24-2013, 07:34 PM
Let the furnace run for 5 minutes. Turn off gas valve, let flame go out, turn it right back on and see if it lights normal

Snapperhead
01-24-2013, 09:02 PM
Let the furnace run for 5 minutes. Turn off gas valve, let flame go out, turn it right back on and see if it lights normal
ahh .... you are bypassing the valve this way , checking to see if valve is opening too slow , good idea !

chrisevansac
01-24-2013, 09:11 PM
valve was not replaced. it was original

chrisevansac
01-24-2013, 09:15 PM
it will light normal because the inducer i still running. it lights normal when i cut the switch off and back on before the inducer has time to completely stop.

gravity
01-24-2013, 09:56 PM
pull the flue pipe off and try it from a dead stop and then while its running. check the runners and make sure they are clean.

check the manifold. there could be lots of spiderwebs in it.