What I've got is a Trane Tracker (touch screen) controling 2 gas pack's single zone & one larger gaspack with 5 vav zones.
My problem is the control panel wont let me change the zone settings (larger unit). I have it set up to disable local setpoints and am programing zone setpoints from the panel, it is now at 70 and 72 for the zones. I tried to open that to 68 & 74 but it wont let me. I put in my password and it will let me change them but when it comes back to the zone status screen it's the same as before. I looked at the global setpoints (if that could cause this) and the window is big enough for these setpoints.
any help??
Thanks

qtip
12-19-2006, 07:26 PM
Check then Min/Max cooling and heating setpoints.

jeepfrk9
12-20-2006, 12:59 AM
I thought I looked at that, Can I preform all functions from the screen or do I need to use the trane software?

jeepfrk9
12-20-2006, 08:32 PM
someone out there knows the answer to this.....please help

supertek65
12-20-2006, 08:39 PM
You might post this on commercial hvac
{hvacowboy} can answer this.
but I do not think he goes to controls

qtip
12-21-2006, 06:56 AM
Originally posted by qtip
Check then Min/Max cooling and heating setpoints.

core
12-21-2006, 07:42 AM
On your larger zone with VAV boxes, If I remember, you have to disable the thumbwheels on the Zone sensors first.

Then you can set zone temps.

Core

jc47
12-21-2006, 12:42 PM
Are you talking about setpoints that would normally be set at the unit controller and you want to control them from the tracker panel; or are these thumbwheel setpoints?

Unregistered
12-22-2006, 04:37 PM
want I want to do is set the zone setpoints for 4 of the 5 vav zones from the panel and have 1 local setpoint from sensor.

gman994
12-23-2006, 02:45 PM
It's been about a year and a half since I've done one of these jobs, and it had quite a few zone systems and single zone units on it. The zone systems were subsystems operating on the comm 4 networks, and the Trackers' (all 3 of which were max'd out) operated on the comm 5 network. We set all of the zone system parameters up on the Varitrac/Varitrane control panels, which by the way , will accommodate the same touchscreen that's on the Tracker or can be setup using their own software that they send free with each panel. There's a bit more to it, but you might want to tansfer the screen to the zone panel and see if that gets you where you need to be. ---gman

traneman666
01-11-2007, 10:39 PM
You need the Trane software to change the global setting I believe.
Get the computer out and hook up then yu will be able to get at everything.