12-17-2006, 09:50 PM
Controller-ASVAV111-1 using the phone jack at controller and terminals at sensor.
Problem-Getting the W/C adj input. Changed sensor, verified continuity and recrimped wires to phone jack but continue to recieve ???? as input . Any suggestions on what to look for?
controlgeek
12-18-2006, 09:16 AM
1. Check and make sure the Q/A in the programming is answered to have a W/C adjust.
2. If the W/C is only unreliable at high or low end calibrate resistance. The W/C adjust is a 0-1660 ohm by default but the actual stat you have could be a little different.
controls_tech
12-18-2006, 09:31 AM
A little troubleshooting trick I like to use to help isolate problems ...
Grab a known good network cable and a known good stat, and use that to plug in right at the controller.
rleo49
12-18-2006, 06:45 PM
It would help to reconnect the phone jack. OOPPS. It was the last thing I did on Friday and forgot to plug it back in after I had crimped the connector. I didn't check it at the work station until today and I had ???? marks on the room temperature as well. Plugged it in and all is well. Thats the second time I've had problems with bad crimps (by others). Thanks for the input.
simux
12-23-2006, 05:29 AM
They have these new Cat 5 connectors that have an EZ designation. They allow you to extend the wires through and avoid problems. Straight up I wouldn't use anything else!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!!!!!!!!!!!!!!