01-14-2013, 04:36 AM
Hi guys..i have came across a different Behaviour of Current measurement device im working on Single Screw Compressor Chiller.With starting method of soft starter so in that 3 Phase wire goes direct to 3 terinal and to co plete the circuit other goes via SCR and Contactor.

NOw the problem im facing is when i measurement current before contactor im getting as normal at full load 130A but when i take after contactor its showing only 70A this is only of a single phase current.


So anybody could help?

malcor
01-15-2013, 07:27 PM
You are seeing the measurement error of your meter. Use one with true RMS and the readings will make more sense.

mayank
01-15-2013, 08:26 PM
ok 1 more question why i cant use 2 or 3 wire in a clamp meter to measure current

gassyplumber
01-15-2013, 08:28 PM
Don't the magnetic fields cancel each other out as far as the meter can read

malcor
01-15-2013, 09:14 PM
ok 1 more question why i cant use 2 or 3 wire in a clamp meter to measure current

The current would need to be in phase (or in sync) between each wire for the meter to read the combined current. Otherwise, as mentioned already, the interaction of the 'out of phase' magnetic fields would give you a false measurement.

Nuclrchiller
01-16-2013, 09:23 AM
The difference you are seeing could be because of where you are putting your meter clamp. If the chiller starter module is electrically located "inside the delta", you may be taking the first reading on 1 of 3 incoming leads, and the second reading on 1 of 6 motor leads. Let's see if we can get a site moderator to move this discussion to the "chillers pro" section. It will be more likely to be seen by more people with experience on this type equipment. Also, the model number and serial number will help people to give you better and more accurate information. And welcome, Mayank.

Chris_Worthington
01-16-2013, 09:36 AM
Thread relocated to the Chiller section of the site.

mayank
01-16-2013, 10:37 AM
347451thank you for your reply Let me explain some detail im using HSA3221A Single Screw Compressor by J &E Hall,and yes motor is in delta connected have uploaded a pic to explain some more detail .Actualy what im measuring is The same phase wire like an example Red wire before contactor and after Contactor i am not getting sum of current.So any body could help me now?

Nuclrchiller
01-16-2013, 11:17 AM
Can you highlight, or indicate in some way, exactly where on this pic you are placing your meter clamp? And, where the pic shows "FUSE", is that actually where the starter module, or contactor, is?

Nuclrchiller
01-16-2013, 11:21 AM
It would be even more helpful if you could show pics of you, or whoever, actually measuring the current on the starter itself.

RichardL
01-16-2013, 06:33 PM
It would be even more helpful if you could show pics of you, or whoever, actually measuring the current on the starter itself.

Now thats funny....LOL

Reading "One" leg on a six-lead motor should give you a reading of 58% of the actual motor current. "NOT" 50%....I digress in stating the reasoning behind this.

Carrene #2
01-16-2013, 08:07 PM
Before you take picture, make sure you have a filter on the lens that will be good to take picture of ARC Welding.
Just in case. At least if anything goes wrong, we might be able to tell you what you did wrong.

CCSPIERCE
01-16-2013, 09:20 PM
Don't use a electronic flash on the camera to take a picture of a solid state starter. Some drives will shut down due to the energy flash. I don't know why but i have seen it happen.

jayguy
01-16-2013, 10:07 PM
Don't use a electronic flash on the camera to take a picture of a solid state starter. Some drives will shut down due to the energy flash. I don't know why but i have seen it happen.

what brand? i want to try that!

Nuclrchiller
01-17-2013, 08:55 AM
Now thats funny....LOL

Reading "One" leg on a six-lead motor should give you a reading of 58% of the actual motor current. "NOT" 50%....I digress in stating the reasoning behind this.

Not sure why that's funny, Richard, but it wouldn't be the first time a joke has gone over my head. Even one of my own.... I was concerned that the OP would not be successful in indicating an actual location as a location on the drawing. I hope that statement makes sense.

mayank
01-17-2013, 10:30 AM
Hey guys why you all diverting from the topic.I am here to get a solution but you started your convesation.I have alreday uploded the pic of the concerned part.

Nuclrchiller
01-17-2013, 12:07 PM
It is very important to measure current at the right locations. You want to be sure that you are comparing the current on the 3 separate phases to each other, or the current on the 6 motor leads to each other. You may have been comparing the current on 1 of the phases with the current on 1 of the motor leads. They will not match. See RichardL's statement above.