View Full Version : Janitrol gas valve voltage
ParamountAir
01-06-2013, 03:53 PM
Issue with Janitrol furnace --
Goes through normal sequence on call for heat - inducer on, pressure switch closes, HSI glows, then gas valve doesnt open. Interesting that the valve has 15-16V consistently until board calls for main valve to open, then 26V at the valve for a few seconds. The 15-16v is to chassis ground and ground on the valve terminal.
I thought there would be no voltage on the valve until a call from the board, thoughts?
pacnw
01-06-2013, 04:41 PM
safety or bad valve or loose connection or bad board or?
Ductfisher
01-06-2013, 04:45 PM
What is your inlet gas pressure? LP or Natural? If you have good inlet gas pressure and no outlet pressure when there is 24 volts across the gas valve coil then the gas valve is bad.
billg
01-06-2013, 04:53 PM
I think it's a bad valve.
Joehvac25
01-06-2013, 05:14 PM
Double Check with the manometer the out let pressure. If you have 24v and no outlet pressure then well you get it. First verify you have inlet pressure though
VTP99
01-06-2013, 05:26 PM
[QUOTE=ParamountAir;14929331]Issue with Janitrol furnace --
Interesting that the valve has 15-16V consistently until board calls for main valve to open, then 26V at the valve for a few seconds.
Something seems fishy here. Sounds like some kind of back feed. Are you sure your transformer is not weak ? I would think that the ignition board would not leak voltage till a call for the main valve. How many wires go to the valve ?
Joehvac25
01-06-2013, 05:33 PM
[QUOTE=ParamountAir;14929331]Issue with Janitrol furnace --
Interesting that the valve has 15-16V consistently until board calls for main valve to open, then 26V at the valve for a few seconds.
Something seems fishy here. Sounds like some kind of back feed. Are you sure your transformer is not weak ? I would think that the ignition board would not leak voltage till a call for the main valve. How many wires go to the valve ?
I bet it's a false reading, one other thing is look for the cracks on top of hx
billg
01-06-2013, 07:02 PM
The coil in the gas valve is open, once you change it the 15-16 volts will go away and it will function when it gets 24 volts.
ParamountAir
01-06-2013, 07:04 PM
Yes, definitely something fishy. I must have measured it started the unit 10 times and measured voltage to make sure my readings were correct. There are 3 terminals on the valve, MV, PV (factory jumped) and C. Where could the 15 volts be coming from?
Thanks!
craig1
01-06-2013, 07:36 PM
There are 3 terminals on the valve, MV, PV (factory jumped) and C. Where could the 15 volts be coming from?
Thanks!
the 15 volts is phantom voltage. When you have a wire connected to nothing (open relay on one end, broken gas valve on other) Voltage will be induced in it just by its proximity to other wires with current flowing in them.
If you put any kind of load on the wire its voltage will drop to 0
chaard
01-06-2013, 08:00 PM
It's not uncommon to see the 24v split across the secondary of the transformer. 12v on one side to ground. 14v on other leg to ground. Together 26v when load is applied.
billg
01-06-2013, 08:06 PM
On Goodman common side of 24 volt transformer winding is grounded to chassis.
chaard
01-06-2013, 08:12 PM
I thought that after I posted. But it does happen, especially on 240v units.
I have come across 2 different units that was 120v to ground on secondary side with no load. 24v with load. Still have never figured that out.
ParamountAir
01-06-2013, 09:06 PM
@ Ductfisher - 8.8 IWC inlet, nat gas 24V across coil.
ParamountAir
01-06-2013, 09:07 PM
Thanks for the replys, I will pick up a valve in the AM
hurtinhvac
01-06-2013, 09:34 PM
If your safeties are holding steady all the way thru to the HSI being energized (the pressure switch is the only one likely to drop out and cause issues at the beginning of a cycle, the rest would not permit any action at all), you have 24 volts across the gas valve for a couple seconds until trial for ignition fails, you hear no click of the valve, or even if it clicks (or chatters) and you smell no gas...
90% of the time it's a bad valve. Just make sure you have gas service. Ignore goofy low voltage readings, they serve no purpose unless you are in controls.
Not exactly a RSES SAM...but it's been my experience.
Cosmicmuffin
01-07-2013, 08:43 AM
Great info... I made up a test 24v. Transformer.ext. cord to 115v / two jumper wires. Eliminates quessing board wiring! I have seen 24v to valve,but if its not grounded thru another switch it "wont" open! Note; clicking of valve is not always accurate either..Goodmans latest bulletin states both Hi And Low side power is needed to open gas valve in two stage models.an auditable noise is no longer a true test!
Cosmicmuffin
01-07-2013, 08:52 AM
I have had two calls this year same thing.H.S.I would glow but NOT lite the Nat. Gas. I now always test with an open flame "Torch". Repositioning HSI...,or replacement have been my remedy.But to be honest...,not sure why! No call backs yet!
VTP99
01-07-2013, 07:34 PM
[QUOTE=Cosmicmuffin;14933661] I now always test with an open flame "Torch".
Yes...This is a very good test to fool the board and check your gas valve. I would try this if you have not yet. Keep us posted with the outcome.
hurtinhvac
01-07-2013, 08:30 PM
[QUOTE=Cosmicmuffin;14933661] I now always test with an open flame "Torch".
Yes...This is a very good test to fool the board and check your gas valve. I would try this if you have not yet. Keep us posted with the outcome.
Surely you jest...
VTP99
01-07-2013, 08:38 PM
Surely you jest...
Nope....serious as a heart attack !
Core_d
01-07-2013, 09:38 PM
Ever check if that 16v was comin outta the board?
hurtinhvac
01-07-2013, 09:40 PM
Nope....serious as a heart attack !
{sigh}
VTP99
01-07-2013, 09:49 PM
{sigh}
I also sometimes do this to bleed the air from the line if I had to open it for a repairs. Just last night I started up a 12 ton Carrier RTU. I had no air in the line up to the shut off valve. So the only trapped air was from that point to the burner. It took about 10 times of letting it work the air out before it lite. I was just getting ready to get my torch when it finally hit. Had I had my torch handy it would have been one time.
timjimbob
01-08-2013, 07:38 AM
Modern digital volt meters use very little current. (loading the circuit)
Have you ohmed the gas valve coil? Open or bad winding would not load the GV circuit enough to bring voltage to zero.
hurtinhvac
01-08-2013, 09:09 PM
Had I had my torch handy it would have been one time.
Got that right...one and done.
ParamountAir
01-08-2013, 11:13 PM
Gas valve replaced....works perfect!