hey need some help, I have a york old faithful gas unit where the rollout limit had tripped, I had the call today, it has only done it one time so far, but I just changed the gas valve out 2 weeks ago, just didnt want to miss something, I am not a DIY'er, I am a contractor

bama 101
11-28-2006, 09:31 PM
You will have to register to get help around here
.....Sorry.........


I'm not a bad guy just following the rules

tinknocker service tech
11-28-2006, 09:37 PM
tripping on roll out 90 percent chance cracked heat exchanger

4l530
11-28-2006, 09:40 PM
So after (I assume) you reset the rollout...then what happened? Do you have any other info as to readings or anything?
A tripped rollout ain't a good sign.
How old is this thing? This rollout, its over the burners or in the collector box, or...?

ngerrald
11-28-2006, 09:41 PM
what is the best way to test for a cracked heat exchanger, I read several books and still cant get a good answer?

ngerrald
11-28-2006, 09:43 PM
after I reset the limit, I turned the heater on and it did not roll out, I tested the unit about 10 times, the limit is on the collector box

4l530
11-28-2006, 09:52 PM
Sounds like the chimney backdrafted, if this is an old gravity draft model
Probably would be prudent to check that it's not partially blocked or something
Sometimes that kind of thing just happens, if it's excessively windy.

24/7mechanical
11-28-2006, 09:55 PM
After changing the gas valve, did you check to outlet gas pressure?

ngerrald
11-28-2006, 09:58 PM
yes i did check the outlet pressure, checked out...