View Full Version : Trane XL19i



jmichi
11-28-2006, 05:09 PM
Can some confirm that the Trane XL19i heat pump, when in heat mode, will always have the its fan running on high speed ? That is what the Trane technician told me. When in cooling, the fan works in two speeds, along with the two compressors
Thanks

klabkebash
11-28-2006, 05:42 PM
well it claims to have 3-stage heating.

see:

http://trane.com/residential/products/HeatPumps/xl19i.aspx

Maybe he didn't want to change the thermostat or indoor AHU

too tall terry
11-28-2006, 05:48 PM
can't confirm that it always will,but it should be......if it is not,you have a problem.....if memory serves me,the t-stat must recieve a call on the fan terminal to kick the blower up to second stage/higher speed.....if this is not happening and you are sure the second stage compressor is in operation.......call a qualified service tech,.....good luck!!!!!

jmichi
11-28-2006, 06:26 PM
This is exactly what is happening. Do you know why does the blower works in two speeds for cooling but only on high speed for heating ? it is certainly noisier

BaldLoonie
11-28-2006, 06:52 PM
I believe the OP is talking about the outdoor fan, not indoors. I do not know the answer but running on high all the time in heating makes sense, trying to get every lick of heat it can. Mark, do you know?

jmichi
11-28-2006, 07:02 PM
Yes, I am referring to the blower on the outside unit

mark beiser
11-28-2006, 07:31 PM
The outdoor fan on XL19i heat pumps runs at high speed for both stages in the heating mode. It does that to maximize 1st stage heating capacity.

emcoasthvacr
11-28-2006, 08:00 PM
Check my understanding mark:

So in the heating mode during the 1st stage, the fan pulls available heat to the evaporator(outdoor coil during heating), and the 2nd or 3rd stage is left to the auxillary.

Since the outdoor fan stops during the defrost cycle(at this time a heat pump goes into the cooling mode and stops the outdoor fan), is this the only time the outdoor fan will stop during the heating cycle of a heat pump?

Thanks.


Originally posted by mark beiser
The outdoor fan on XL19i heat pumps runs at high speed for both stages in the heating mode. It does that to maximize 1st stage heating capacity.

mark beiser
11-28-2006, 09:19 PM
2nd stage is the bigger compressor, 3rd stage is the aux heat.

You are correct in that the only time the fan stops during a call for heat is when the unit is in defrost.

emcoasthvacr
11-28-2006, 09:57 PM
Thanks


Originally posted by mark beiser
2nd stage is the bigger compressor, 3rd stage is the aux heat.

You are correct in that the only time the fan stops during a call for heat is when the unit is in defrost.

jmichi
11-29-2006, 11:05 PM
thank you all