View Full Version : Sparks coming from air handler



myhvacx
12-17-2012, 09:57 PM
18000 btu upflow closet unit w/electric heater,
call for cooling had just kicked in when sparks came out of the air handler, it lasted approximately 1 minute.
turned breaker off and checked inside wiring, everything looked dry and in good shape, tight.
checked breaker box and found no abnormalities..

any ideas?

Mr Bill
12-17-2012, 10:19 PM
My guess would be you had some heat strips burn into or break and fell against the chassis.

myhvacx
12-18-2012, 08:54 AM
338281338291
Something I missed, there was some steam coming from a closeby shower room at the time this happened.

toocoolforschool
12-18-2012, 09:16 AM
You mean you watched sparks fly for a minute??? yikes.

myhvacx
12-18-2012, 09:21 AM
yah, well I didn't see the sparks myself, the first picture above shows the corner of the air handler, if you look closely you can see the burnt screw below the tape... Further testament of the presence of the sparks is when I turned breaker off and felt the warmth just on that one part of the handler, felt like 85 degrees.

toocoolforschool
12-18-2012, 10:13 AM
You have to find the short which is somewhere in the unit.

Mr Bill
12-18-2012, 10:38 AM
if you look closely you can see the burnt screw below the tape...

Looks to me like "from what I can see in that small picture" the plastic terminal block may have got hot due to loose connection, and did a semi meltdown, and the hot wires may have touched the chassis on the back side of the terminal block.