I have a Rheem furnace with 5 inshot burners in it. Sometimes only the burner on the far right comes on and after about 5 seconds the unit shuts down then the fan only runs. I have checked and cleaned the crossovers and aligned the burners and checked the gas pressures into valve 12"wc and out is 11"wc. can anyone help me, this is frustrating>
tinner73
11-01-2006, 07:57 PM
12" wc?
tbonebilly
11-01-2006, 08:01 PM
12"wc is 12 inches of water colume gas pressure on LPG
hvac hero
11-01-2006, 09:58 PM
did u check the orfices to make sure a spider web didnt clog up the 2nd one?
jvwinn
11-01-2006, 10:57 PM
How many volts do you have at the gas valve?
comfortdoc
11-01-2006, 11:46 PM
Shut the furnace of and call an experienced service tech to test and diagnose the system. This can be very dangerous especially with LPG.
docholiday
11-02-2006, 03:54 PM
Why did you set it up for 11"? (I realize it's LP) Did you read that in a manual somewhere? 'Cause it isnt anywhere in the manual for your furnace.
doublevision1
11-02-2006, 09:31 PM
CHECK ORFICES AT BEGINNG OF BURNERS TAKE THEM OUT AND CHECK FOR SPIDER WEBS INSIDE
tbonebilly
11-06-2006, 05:00 PM
Manual says 12-14 inches water colum.
docholiday
11-06-2006, 06:07 PM
inlet maybe, not outlet.