10-16-2006, 08:05 PM
I have inherited a 30gx ( tonnage??? 4 compressor) that has started to randomly trip low oil level alarms on circuit B repeatedly since the out door temp started falling.

I added some oil after recovering it back as per manual and it is still doing it.

I do know that the minimum load kit and the oil re-route kit for the comps has been recently installed back in the summer (July)

I have checked the level and it appears OK.

The oil heaters are a-OK

The machine appears to be operating normal when I have checked it and logged it out. All the numbers look OK.
I did change the loading from staged to equal as I would notice B ran a lot at minimum load and felt this may have been part of the problem.

This is a process chiller not comfort cooling.

Has anyone had any problems with the oil level switches ,the kind that screw in the bottom of the separator?

Any ideas would be appreciated.

dodds
10-17-2006, 06:22 AM
What is the chilled water set point?
If the Chilled water set point is too high the unit will short cycle and cause the oil to migrate

mikeacman
10-17-2006, 07:40 AM
48 degrees F, It doesn't short cycle but another tech set it up for A to lead so B runs at very low load for extended periods.

I do not like this and am going back today to give it a good going over again and look really hard at the config. The tech that was working on it is now in IRAQ so I can't really quiz him on anything but , I do know it has always been a problem child.

lugnut
05-01-2008, 08:46 PM
Did you ever learn the cause of the low oil alarms?

Gibbo
05-04-2008, 09:50 AM
If you are sure the oil level is ok then the problem is likely the oil level switch connections or the oil level switch.

HeatXfer
09-06-2008, 12:11 PM
Coming late the party. Carrier's fix for low oil faults is usually to add more oil until the problem goes away, which can result in even more problems. If your process load is steady, and condenser press/temp control is good, there shouldn't be a problem.

Continuous low ambient operation and short-cycling are certainly possibilities, but here are two more I've seen to consider:

#1 Bad oil separator - Observe the sight glass before the EXV (or the Economizer), if you see white foam and the liquid line is cool, you've got too much oil carryover through the condenser. This is an indication of a torn or collapsed arresting screen in the oil separator. The only fix for this is to replace the separator (sorry).

#2 Stuck oil solenoid relay - An oil solenoid valve that is energized or stuck open on a non-operating comp will allow oil to pass directly through that comp and into the evaporator while the other comp in the circuit is running. During low-load conditions more oil will pass into the evaporator through the oil valve that will be returned to the separator, resulting in low oil levels.

There are two causes: 1) the valve is simply stuck open, or, 2) The oil solenoid relay on the CPM (Comp protection module) is burned closed, continuously energizing the oil solenoid valve.

While the chiller is off, check the oil solenoids on all comps. If any comp has an energized oil solenoid, that most likely means you've got a bad oil relay on that comp's CPM.

The CPMs are found in the control panel, they are the two 'exposed' circuit boards (approx 5"x10"). The 'A1' & 'A2' comp connections will either be at the top or the left side of each CPM board respectively, depending if they're mounted vertically or horizontally. The 'B' comp connections will be at the bottom or right side of each board.

Verify proper oil solenoid operation by enabling manual operation and cycling the solenoid.

If you change CPMs, don't forget to move the configuration header(s) from the old board to the new.

chiller rob
09-08-2008, 09:46 PM
nice post heatxfer...

i have found bad oil level switchs and tried to dance aound it before condemning...

also consider your base load... equal loading may not be a good idea based on low ambient considerations...

good luck

rob_servicetech
09-09-2008, 07:03 PM
Also check delta P of internal and external oil filters, I have found that you will get different alarms related to oil as they become restricted. It wont always give low oil pressure alarms

stanbyyourword
09-10-2008, 03:23 AM
was going to post this a couple months ago for some input from carrier pros

, had a crazy high oild diff alarm on 30gx which has since gone to quote , odd building/customer , im not that familiar w these chillers , but external and internal oil filters checked out 100% , and oil trnsducer was changed out new, this is ckt a2 which is common for ckt a1

1, basically this fault was constant , but after a few trips and several
runs i finally found prodialog display going off the roof w diff on a2 reading something like 100psi diff which was 0 or close too , also when this would shoot up all of a sudden would find ckt a1 which ran fine w no oil diff alrams whatsoever shoot up for a few secs to high inaccurate number before a2 running would trip out then a1 would resettle to correct number, hard to catch this especially scrolling thos dialog keypads , i was leaning torwards processor , but didnt know about this calibration aspect , but thing w that is reads accurate at times , any thoughts ? regads stan

Dallas Duster
09-10-2008, 06:52 AM
was going to post this a couple months ago for some input from carrier pros

, had a crazy high oild diff alarm on 30gx which has since gone to quote , odd building/customer , im not that familiar w these chillers , but external and internal oil filters checked out 100% , and oil trnsducer was changed out new, this is ckt a2 which is common for ckt a1

1, basically this fault was constant , but after a few trips and several
runs i finally found prodialog display going off the roof w diff on a2 reading something like 100psi diff which was 0 or close too , also when this would shoot up all of a sudden would find ckt a1 which ran fine w no oil diff alrams whatsoever shoot up for a few secs to high inaccurate number before a2 running would trip out then a1 would resettle to correct number, hard to catch this especially scrolling thos dialog keypads , i was leaning torwards processor , but didnt know about this calibration aspect , but thing w that is reads accurate at times , any thoughts ? regads stan

Have you tried any die-electric grease on the op transducer?Does it happen when moisture is present?

stanbyyourword
09-10-2008, 08:43 AM
nope absolutely dry days and new transducer

Dallas Duster
09-10-2008, 11:21 AM
Do you ever et to see it fluctuate with your guage and actually see the pressure hunt around?

stanbyyourword
09-10-2008, 11:40 AM
nope steady, and good sound cable connections also , maybe ill repost new thread as not to highjack this oiginal , see you there! ;) regards stan

HeatXfer
09-10-2008, 08:50 PM
Are your condenser fans momentarily dropping off?

Are there any radio transmitters on or near the roof, including cell phone antennas? Are there building engineers or maintenance people with older, 2-way radios? SMR ('trunked'), microwave or any older radio system in use near by? - some municipalities use them for their maintenance fleet. They run on 800 & 900mhz, which can cause interference on some solid state systems.

Are there light rail tracks near by, heavy VFD use? Any heavy equipment that cycles on and off in the building? Are there power problems? Do you have 'dirty' power at this building?

Is the battery in the PSIO older than 5years?

It does sound like something is going in the control circuits, and not a 'real' pressure issue.

/Yep, I've seen first hand an old (cir1995) trunked Kenwood 2-way radio temporarily scramble an EXV board for the flowtronic EXVs on an older 30GT.