globe trotter
10-07-2006, 02:23 PM
Help me
Question 1:
Am I correct that Distech has no NVI for heating, cooling setpoints separately in their RTU-L (roof top controller)? The one NVI setpoint that they do have is for the average between the two which really doesn’t tell me anything for sure (NVISetpoint). The VAV-l is the same way.
Is their no way to bind individual heating, cooling, occupied and unoccupied setpoints to the network?
Question2:
On the EC-67 (free prog) it does have an Optimum start however it is bound to the scheduler in the controller. (No way to use an NVI_TOD_event). So I'm stuck using the scheduler in the controller that I can not change setting of from the network (NO NVI for event settings)
Is their any way to use a free prog Optimum start with a schedule I can edit from the network?
[Edited by globe trotter on 10-08-2006 at 01:44 AM]