I have a customer with a York millenium vav rooftop unit. It is around two years old. The unit has Johnson unt controllers (factory installed) and the building has vav boxes with lon controllers on them. I want to reset the supply air based on worst zone, is there a way to get the signal from the lon boxes to the N2 controller. There was a lon card originally shipped with this unit but York has said it will not work.The unt uses a single space temp for reset but if I can use the worst zone I think I can achieve some significant energy savings. I was thinking of putting in a programmable controller and bringing all the space temps into it and writing some logic to find the greatest deviation from setpoint and reset supply air based on that and using a 0 to 10 out to the unt, I am not sure if the unt will accept it or not (these are labelled as Synthesis controllers by York but are a unt with an expansion board.
Any other suggestions would be great.