PDA

View Full Version : eev problem



orland25
10-02-2006, 09:06 PM
Hi friends: We have a little problem with a EEV on YCAL0114 YORK SYSTEMS.6 scroll compressor 3 per systems' the problem is all times goes to Low Superheat" ok Low Superheat drop to -2F or the eev pilot solenoid close 10 times in 2 minutes" ANY IDEA PLEASE THANK"" OOP" set-point 36deg (glycol system) subcooling 14 to 17 deg

flange
10-08-2006, 09:27 PM
if the system was not designed or set up to run glycol you will have thesxe types of problems due to reduced heat transfer. you must know concentration of glycol and design for that.