hi.

am looking for a solution to our problem w fan coil. It is rated 25TR serving 3 tenants almost 395sq. m area. The 2 tenants are having 74°F space temp while the 1 where the unit located is exp a 77°F and higher temps. My suspecion is that there is a short circuit in the system causing a warm temp to this area. any good expalnantion will be much appreciated. CHW temps: 53°F supply/62.5°return; CHW press: 25psi supply/19psi return. Unit's return side is almost 1 foot from the wall and it is hanging.

lwarren
09-14-2006, 09:49 AM
Why are you running your chilled water supply temp @ 53 deg. You need to get it down to 42 - 44 deg.

The Saint
09-15-2006, 06:11 AM
Check the following:

Inlet filter/strainer
Fan coil for dirt
Air Filters
Fan cfm, rpm, etc.