has anyone had problems with lennox CB26UH air handlers.we have had several so far.

croft1972
09-04-2006, 08:04 AM
We've found that open return units tend to hold water in them.

sheetmtlman
09-04-2006, 10:27 AM
what's the problem?

Milk man
09-04-2006, 10:31 AM
upflow or downflow?

Trapped or not?

mook531
09-04-2006, 02:18 PM
dont use them...we use cb30's....and no problems with them

scacguy
09-04-2006, 07:18 PM
application is horz/lennox tells us that 3 corners must be raised 1/4 inch to pitch towards corner with drain. a tee must be installed after trap with no cap so it is a vent.lennox says primary pan is only supposed to hold 2 tablespoons of water.several ones with long runs on drainline have installed condensate pumps &still have return boxes with water &wet ceilings.no room for error.they should have seen this being a problem since this is the cheap builders model& installed by subs that dont speak english in trac homes

cde72
09-04-2006, 08:45 PM
Vents after traps are always good, the same reason plumbers must run vents right after traps in DWV. I always vent the tee with a length of 3/4 pipe that extends above the height of the primary pan so that if the drain is clogged between the trap and the "daylight", overflow water comes out of the primary and hopefully into the secondary as opposed to the floor or insulation in a horizontal application.