Have Trane 2 ton Heat pump ( XE1000 - model TWR024C100A2) and 2.5 ton evap coil ( model TWV030B140A1) under high heat load ( Dallas tx -100+ outside) . Gas charge is optimum with superheat at 5F / blower is medium speed of 3 available. Delta-T Heat rise is 16 F at 1650CFM at consenser unit so I'm not getting full 2 ton BTU's heat removal after accounting for fan motor and compressor heat . Evaporator Sticker says orfice was installed. What would be the optimum orifice size for max cooling on this non-TXV evap coil ?? To get more cooling capacity - should I increase blower speed and also increase orfice size as well?? This unit only services part of the house- large master bedroom and bath area only.