View Full Version : Explain once more
esquire
08-26-2006, 08:10 AM
I know that the presuures must be converted to temp for superheat and subcooloing For superheat is the suction line temp read at condenser or evap? For subcoolong is the temp read at condenser or evap. My boss tells me one and another tech tells me another. I'm new and learning in this field but everyone has a different way of doing. Thanks
dirtyboy103us
08-26-2006, 08:31 AM
subcooling is on the liquid side or high side at the condenser
superheat is at the evap or low side at the service valve at or near the compressor
nickellhead
08-26-2006, 08:33 AM
both at the service valves by the compressor
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.