I have an Amana PTAC where the compressor is short cycling?
the compressor comes on for about 5 min then shuts off. if you turn the unit off for a few min then back on the compressor runs again? it is a sealed system and I can't put my gauges on. Any Ideas?

dhaynes
08-22-2006, 07:04 PM
buy a line tap saddle type valve so u can get your guages on........youll just be guessin if u dont know them

robbiesteel
08-22-2006, 07:14 PM
Thanks, I didbuy one, I just havent tried it yet. Not to keen on piercing valves.

dhaynes
08-22-2006, 07:31 PM
u can always put the piercing valve on and trouble shoot the system. If its worth fixing then evacuate the system and braze a couple of stem valves in there

4l530
08-22-2006, 07:47 PM
Seen a bad thermostat make it do that.
Stupid PTACs :mad:

ddog1
08-22-2006, 10:59 PM
Did you check amp on run windings...low or high??

robbiesteel
08-23-2006, 03:47 PM
The compressor was overheating and shutting down. This is a through the wall Amana PTAC. I put the valves on and the pressures seemed fine. Here's where I slap my self. I found the inside of the outer coil was blocked solid with gunk. I cleaned the coil and now the compressor stays on! Doe!
Thanks for everyones help. I'll be comming back for more.