08-20-2006, 01:27 AM
I am working on a dx cooling system running 95# suction & 240# liquid pressures.
Superheat about 20degF. TXV on evap.
I suspected bad compressor valves.
Performed pumpdown and suction pulled down to 0 psi. and held with no problem.
Space temp is 80 deg.outdoor temp 102 deg.

My question is. Can this compressors valves be bad??

dirtyboy103us
08-20-2006, 01:33 AM
need more info than that heat pump strait cool
indoor wet buld dry bulb you know the basics

Milk man
08-20-2006, 01:40 AM
Doubt it since it pumped down.

Take a TD at the evap. Interested to know what the return temp is at the airhandler.

beenthere
08-20-2006, 07:00 AM
First, you should register as a pro, and ask your questions in the pro tech forum.

You should have taken a sc reading.

Sounds more like an under charge, and the txv is wide open, causing the head pressure to be low.

But without more info, no way to tell for sure.

deejoe
08-20-2006, 11:55 AM
Originally posted by dirtyboy103us
need more info than that heat pump strait cool
indoor wet buld dry bulb you know the basics
************************************************** ***********
How about using the PERIODS, (they look like these .....) on your keyboard.
Periods, and commas, can sure help in understanding some postings.

ARPA
08-20-2006, 12:04 PM
Unfortunately, due to site rules (http://hvac-talk.com/vbb/showthread.php?threadid=1241) we as members can not discuss technical issues with the general public.

If however, you are a HVAC/R Technician, please sign up as a professional member by clicking on the contact us button at the bottom of the page and we'll assist you getting signed up in the Pro-Forums.

After you register as a Professional, we’ll move this post over to the ProTech Forum.

Thank you for your cooperation.