RichardL
08-15-2006, 11:59 AM
"Trimming" an absorption chiller that is already on-line is not as easy as measuring the amount of Li-Br...
As the pump seal rings & Labyrinths wear, the charge must be adjusted to compensate for the lower flow of Li-Br to the Generator/Concentrator...
Regardless of make-model-manufacturer there are certain parameters that are virtually identical, with the main, most important being the "Spread" of Li-Br..
The term "Spread" has but one meaning on Absorbers and that is the Strong Sol. vs. Weak Sol. @ full load..
Soooooo.. when Solution pump starts to degrade(Pumping Less) the charge is adjusted to increase the capacity(flow-rate) on the solution pump...
Soooo.. if you find one running say.... a 6-7% spread @ load, you are bordeline with going solid and the flow must be increased either by a complete rebuil of solution pump(s) or temporarily readjusting solution charge to keep chiller on-line until such time a overhaul can be scheduled..
These wonders are not at all like sticking ref. in a Recip. package unit & walking away...
That is why the few Absorber Guru's that are still available are held in high esteem by one and all..
As the pump seal rings & Labyrinths wear, the charge must be adjusted to compensate for the lower flow of Li-Br to the Generator/Concentrator...
Regardless of make-model-manufacturer there are certain parameters that are virtually identical, with the main, most important being the "Spread" of Li-Br..
The term "Spread" has but one meaning on Absorbers and that is the Strong Sol. vs. Weak Sol. @ full load..
Soooooo.. when Solution pump starts to degrade(Pumping Less) the charge is adjusted to increase the capacity(flow-rate) on the solution pump...
Soooo.. if you find one running say.... a 6-7% spread @ load, you are bordeline with going solid and the flow must be increased either by a complete rebuil of solution pump(s) or temporarily readjusting solution charge to keep chiller on-line until such time a overhaul can be scheduled..
These wonders are not at all like sticking ref. in a Recip. package unit & walking away...
That is why the few Absorber Guru's that are still available are held in high esteem by one and all..