PDA

View Full Version : 410a retrofit, do you txv any piping?



wolfstrike
07-09-2012, 09:14 PM
i changed a condensor recently.

i was going to put on a 410a but when i looked in the indoor coil, the liquid line was only about 6" long on the inside and against the door , the suction was about 3" before it left the coil.

the copper (both) came out of the coil about 3" then a 90-degree drop downward.

the piston was in a fitting right at the coil sheet metal wall.

if i put in a txv it would have been right in front of the coil access.

i decided i might get myself into some trouble so i explained it to HO and slapped on an R22 condensor.



anyways, my question for you retrofit pros is, are you able to make the txv retrofit happen in any situation?

Flip14
07-09-2012, 09:22 PM
Yes. You can take your piston out of the fitting and then put it back together. Weld on a txv outside the coil, insulate the liquid line out of the txv AND the txv body itself because it will probably sweat and drip water on whatever is under it.

wolfstrike
07-09-2012, 11:58 PM
perfect info , thanks

BaldLoonie
07-10-2012, 06:17 AM
We don't reuse coils that have had 22 in them on 410 outdoor units. In the rare event the HO won't do it right, we will do a dry unit. But those are few & far between.

hvacvegas
07-10-2012, 09:08 PM
We don't reuse coils that have had 22 in them on 410 outdoor units. In the rare event the HO won't do it right, we will do a dry unit. But those are few & far between.

I thought armstrong had the "honkeytonk horsesh**" (named by myself) method of cleaning evap coils?


Seriously, don't try and use a coil that has had r-22 in it, for 410.

If you want a txv, you should be able to throw it on. Be creative.

wolfstrike
07-10-2012, 10:12 PM
i watched you guys argue about 410a retrofits, 'what's the best way to flush?' , ...now that i told a customer i'd put on a 410a condensor, now you're saying don't do it.

:)

:mad:

the HO insists on doing only the condensor now and claims they could be ready to replace everything else in a few months.
if i slap on an r22 it would be a waste.

...to be honest, i don't trust the 410a, even when everything is proper
:)

hvacvegas
07-10-2012, 10:14 PM
i watched you guys argue about 410a retrofits, 'what's the best way to flush?' , ...now that i told a customer i'd put on a 410a condensor, now you're saying don't do it.

:)

:mad:

the HO insists on doing only the condensor now and claims they could be ready to replace everything else in a few months.
if i slap on an r22 it would be a waste.

...to be honest, i don't trust the 410a, even when everything is proper
:)


I don't think anyone is arguing against a 410a unit.

You'll be tough to find someone here willing to put a 410a unit, on a coil that was used with r-22.

When we say flush, most are speaking specifically about the lineset only.

wolfstrike
07-10-2012, 10:28 PM
i called totaline and they told me "yeah no problem, just put on a txv"
later i called Rheem and they said "we don't recommend it , but everyone is doing it"

:)

oh well, i hope this doesn't turn into a mess

Pete954
07-10-2012, 10:43 PM
speaking of flushing linesets. Had someone tell me that they flush with r-22 and follow with nitro on a full change out to 410a. Theory being that the 22 would push most of the oil and nitro would get the rest. Sounds pretty sketchy. What does everyone think is the best. Not counting a new lineset.

wolfstrike
07-11-2012, 03:23 AM
...with the 13 SEER equipment the coils are so cheap it's not even worth the risk

beenthere
07-11-2012, 08:58 AM
I've put 410A condensers on oils that had been R22 systems. blow them out like I do the line set, put on a R410A TXV, vac and check charge like normal.

marvin
07-11-2012, 02:04 PM
I've put 410A condensers on oils that had been R22 systems. blow them out like I do the line set, put on a R410A TXV, vac and check charge like normal.

ive been doing the same thing with no problems. i even have one operating on an old 10 seer evap. that is holding its own in this 112 deg. weather.

hvacvegas
07-11-2012, 05:37 PM
I've put 410A condensers on oils that had been R22 systems. blow them out like I do the line set, put on a R410A TXV, vac and check charge like normal.

How do you know your hitting all tubes, and not missing a circuit?

beenthere
07-11-2012, 05:51 PM
How do you know your hitting all tubes, and not missing a circuit?


In order to "miss" a circuit. That circuit would have to be restricted. Which would show on start up. And mean they would need to get a new coil then.

You don't need to get every drop of min oil out of the system.

Saturatedpsi
07-11-2012, 08:36 PM
I've put 410A condensers on oils that had been R22 systems. blow them out like I do the line set, put on a R410A TXV, vac and check charge like normal.

Does anyone know for sure, whether or not the mfg(s) would honor a compressor (or any other refrigerant system component) warranty with the 410A/22 mismatch? Or dealt with that situation?

beenthere
07-11-2012, 08:47 PM
Most coils made the last several years have been R410A/R22 coils. So there is no mismatch on many of them.

Haven't had a compressor go out that is on a coil that was used for R22. So never had to file a warranty claim.

wolfstrike
07-12-2012, 02:28 AM
Does anyone know for sure, whether or not the mfg(s) would honor a compressor (or any other refrigerant system component) warranty with the 410A/22 mismatch? Or dealt with that situation?


Rheem dealer told me "everyone is doing it, but we don't want the responsibilty"