View Full Version : 70% humidity at 72 degrees with my Trane XL15i and Hyperion- why so humid?



clydesdale
07-04-2012, 08:34 PM
I have a 2 ton system for my upstairs 1100 sqft condo. It usually keeps the humidity around 50-54%. But it was over 90 here today and I am sure it ran for most of the day. Any idea why it is so humid? It feels fine, but I just checked it out of curiosity at the thermostat and it seems pretty high. THanks

vstech
07-04-2012, 08:48 PM
tight construction can lead to high humidity... as can low loads. a condo could have low loads due to adjacent homes temps...
also, you could have humidity entering from long fan run times, or dryer usage... cooking loads, extra guests etc...

teddy bear
07-04-2012, 08:49 PM
Fan in the "auto" mode or "on"? During high cooling loads, the a/c should be able to maintain <50%RH. A/c needing surface could be. What is the temp/%RH of the supply air to the space?
Regards TB

clydesdale
07-04-2012, 09:05 PM
Teddy bear, I thought the supply air is the air in the house. THe outside air is 80 degrees with 77% humidity. Inside is 72 with 70% humidity. The fan is on auto.

teddy bear
07-04-2012, 10:33 PM
Supply is the air entering the home from the a/c.
Temp/%RH? Sounds like the system is slowly losing capacity.
Regard TB

beenthere
07-04-2012, 10:34 PM
The supply air, is the air blowing out of the registers.

Thermostat's humidity sensor may be off. 70%RH at 72 would feel very uncomfortable.

clydesdale
07-05-2012, 06:04 AM
When I woke up this morning it was still 72 degrees, but 51% humidity. Please explain. Thanks.

beenthere
07-05-2012, 06:10 AM
Get another hydrotherm, and place it near your thermostat.