As part of the negotiations for purchasing our house an HVAC company replaced the AC coil above our furnace, balancing it with the outside unit, retarding coils etc. It all looks good etc but I'm concerned that the static pressure drop of the unit is too high for the blower in our furnace. My question is whether they should/could have known that and whether I have any reasonable recourse?
The ducts are a mess and I'm getting quotes to fix those. As part of that process we had a Manual J done (assuming some improved insulation) and apparently we need 1150 cfm. The manual for the furnace says that the blower can deliver 1150 cfm @ 0.545 IWC. It's unclear if that was tested with a filter or not (no footnotes). FWIW it's a RUUD Silhouette II Model: UGPH-05EAUER.
The pressure drop for the new coil Wet @ 1150 is 0.415 (Goodman Model#: CAPF3636A6DB). Accounting for grills etc takes another 0.09 IWC.
If the blower was tested with a filter in place (which filter?) then the Available Static Pressure for the ducting appears to be 0.04 (0.545 - 0.415 - 0.09 = 0.04)
If the blower wasn't tested with a filter it seems that a reasonable estimate for the "True Blue" filters we are using (24"x12") at end of return is something like 0.08 (based on this link http://www.texairfilters.com/news/testsonpressuredrop.htm adjusting for smaller size filter). That would imply that there is no available static pressure @ 1150 and best approach (short of replacing the furnace) is to replace the fan with a higher powered one.
Presumably at the moment we're getting much less cfm, which accords with cooling difficulties throughout the house, but particularly at the end of the longest runs.
So that's a long way of asking: should I be annoyed with the company that put this coil in the system? On one hand they might have been operating with some assumption of less cfm needed (at 900 cfms the coil only has as a drop of 0.28), on the other hand I think it was irresponsible to specify this without knowing the pressure requirements of the system. Or should I just ignore them, work with what we have and just get some quotes for a replacement blower?
Thanks,
James
The ducts are a mess and I'm getting quotes to fix those. As part of that process we had a Manual J done (assuming some improved insulation) and apparently we need 1150 cfm. The manual for the furnace says that the blower can deliver 1150 cfm @ 0.545 IWC. It's unclear if that was tested with a filter or not (no footnotes). FWIW it's a RUUD Silhouette II Model: UGPH-05EAUER.
The pressure drop for the new coil Wet @ 1150 is 0.415 (Goodman Model#: CAPF3636A6DB). Accounting for grills etc takes another 0.09 IWC.
If the blower was tested with a filter in place (which filter?) then the Available Static Pressure for the ducting appears to be 0.04 (0.545 - 0.415 - 0.09 = 0.04)
If the blower wasn't tested with a filter it seems that a reasonable estimate for the "True Blue" filters we are using (24"x12") at end of return is something like 0.08 (based on this link http://www.texairfilters.com/news/testsonpressuredrop.htm adjusting for smaller size filter). That would imply that there is no available static pressure @ 1150 and best approach (short of replacing the furnace) is to replace the fan with a higher powered one.
Presumably at the moment we're getting much less cfm, which accords with cooling difficulties throughout the house, but particularly at the end of the longest runs.
So that's a long way of asking: should I be annoyed with the company that put this coil in the system? On one hand they might have been operating with some assumption of less cfm needed (at 900 cfms the coil only has as a drop of 0.28), on the other hand I think it was irresponsible to specify this without knowing the pressure requirements of the system. Or should I just ignore them, work with what we have and just get some quotes for a replacement blower?
Thanks,
James