View Full Version : McQuay -ALR160
hvac tim
08-01-2006, 06:50 PM
I had a alarm of bad volt ratio sensor. I have it down to 5VDC press. transducers, signal converter, CT1, RES1. I do not have a manual.help!!!!Thanks
hvac tim
08-01-2006, 07:07 PM
I am getting one sometime tomm... just thought someone would have an answer before i get one. thanks
sabre11134
08-01-2006, 07:24 PM
you can get the manual on their website in pdf form.
http://www.mcquay.com/mcquaybiz/literature/lit_ch_wc/IMOM/om127.pdf
[Edited by sabre11134 on 08-01-2006 at 07:34 PM]
hvac tim
08-01-2006, 08:03 PM
I found it on their web site. Thanks alot. it is the 5VDC pressure transducer.
refrtech
08-01-2006, 09:03 PM
Try replacing the suction transducer . ;)
Make sure it is mounted horizontal to.
hvac tim
08-01-2006, 09:10 PM
they are factory mounted horiz. I have 2 suct. and 2 disch. and it is an intermit. prob.
mqfs-no
08-01-2006, 10:20 PM
Check where the regulated 5vdc comes out of the MCB then check all tranducers for a good connection and for no corrosion and moisture. Then check the wire nut where all of the tranducers get there power and last thing check all connections on the ADI board. If this dose not work call your local McQuay Factory Service they should be able to help.