BlueEyedGuy50
06-25-2012, 07:53 PM
Hi Pros !
I have a 20 year old Bryant split system: evaporator coil in the attic, condenser unit outside. Yesterday afternoon, I noticed "not as cool" air coming from the registers. I could hear the blower inside still running, but walked outside and observed that the condenser fan had stopped. I then shut down the power at the thermostat, waited about 10 minutes, then turned it back on. Still no fan movement, but the compressor was working and unit was heating up quickly. So, power off ! 5 years ago, a similar incident resulted in replacing the capacitor (noted on the invoice as a dual circuit running phase shifter). My questions: 1) What is the normal life of a fan motor? 2) What is the normal life of a capacitor ? I'm calling a contractor within the next day or so.
All feedback is appreciated, thanks !
NY2GA01
06-25-2012, 08:11 PM
There are only two guarantees in life, you are born, and you are going to die, that's it.
No such thing as "normal life" in anything.
udarrell
06-25-2012, 08:15 PM
IMO, you can't quote an average life-span of a fan motor or a capacitor because I've seen tremendous differences in their life-spans.
I always only carried 440 volt capacitors with a variation of MFD Ratings; less inventory to cover the various MFD Ratings.
The 440's sub for 370-volt capacitors because they simply have a higher insulation factor with which to withstand higher voltages.
NY2GA01
06-25-2012, 08:41 PM
IMO, you can't quote an average life-span of a fan motor or a capacitor because I've seen tremendous differences in their life-spans.
The 440's sub for 370-volt capacitors because they simply have a higher insulation factor with which to withstand higher voltages.
I have not seen any differences betweeen the 440s and the 370s life spans, they go out just the same.
catmanacman
06-26-2012, 05:50 AM
I would think the fan motor is past a normal life ,as for capacitors the cheap china crap that is widly used dont last .also at 20 yrs might be time to look for something thatnis more efficient
BlueEyedGuy50
06-26-2012, 09:07 PM
Thanks Guys,
I'll let you know what the contractor discovers.
Cooked
06-26-2012, 09:32 PM
............5 years ago, a similar incident resulted in replacing the capacitor (noted on the invoice as a dual circuit running phase shifter).............
Now that's funny right there.
Cooked
06-26-2012, 09:36 PM
Make sure whoever changes the capacitor
You're fixing to get 50 whacks with a wet noodle.
beenthere
06-26-2012, 09:41 PM
yunggun, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.
You can find the rules for posting and qualifications here (http://hvac-talk.com/vbb/showthread.php?t=957002).
Further infractions may result in loss of posting privileges.
BlueEyedGuy50
06-29-2012, 05:59 AM
Good Morning Pros,
Problem solved: contractor diagnosed bad capacitor and replaced. Yes Catmanacman, capacitor made by our Chinese brothers and sisters. He said these are liquid filled but there are other more expensive types that last longer. I'm glad of course that the fan is OK as the cost for the visit would have doubled. I'll search the threads for capacitor 101 basics. Service call by the tech was worth it----temp will exceed 100 degrees today and this weekend in the Southeast.