View Full Version : liquid line sweat
wasson
07-17-2006, 10:33 PM
I have a liquid line sweating from the wall plate to air handler. It is dry back to condenser.Don't know if it is drier or compressor valves.Please help.THANKS!
amickracing
07-17-2006, 10:56 PM
If it truly is the liquid line that's sweating you're in for a major fix.
Step away from the unit and get a phone book.. best tool to fix something like that.
wasson
07-17-2006, 11:03 PM
It's truly sweating.Pressures are 64/240.Do you know GOOD pump down test.If drier's clogged wouldn't it sweat at drier and could a weak vavle cause this.
Chill
07-17-2006, 11:15 PM
what's the temp drop across drier? While your at it, take SH and SC measurements. I don't understand your reasoning on compressor valve plate being the problem?
bobr42
07-17-2006, 11:27 PM
RESTRICTON
wasson
07-17-2006, 11:30 PM
Lost capacity,or am I way off?
lawdawg0321
07-17-2006, 11:38 PM
you have a bad restriction. you need to blow the line out with nitrogen
will 2
07-17-2006, 11:47 PM
And due to site rules.........
Regardless of what your profile says.
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.