duke of earl
07-05-2006, 10:39 PM
Went on a service call this morning to check out a small refer unit that was installed to cool a concrete lab.Found HP switch tripped. Reset switch and checked Suction 70PSIG,
superheat at evaporator 30 degrees, Discharge 250 psig, subcooling 20 degrees, OAT 85 degrees, EAT 75 degrees. The lab is to stay humid for concrete testing I was told after scratching my head a while. I was expecting 8-10 degrees of superheat without really thinking about this process. I learned that we were only doing sensible heat removal, thus explaining the high superheat. I'm glad the txv was non-adjustable so I wouldn't screw it up. Just reminded to ask questions before making assumptions. An explanation of operation laminated and mounted on the side of the unit would be perfect for future service calls cause I can see the next guy going through the same confusion I went through.
superheat at evaporator 30 degrees, Discharge 250 psig, subcooling 20 degrees, OAT 85 degrees, EAT 75 degrees. The lab is to stay humid for concrete testing I was told after scratching my head a while. I was expecting 8-10 degrees of superheat without really thinking about this process. I learned that we were only doing sensible heat removal, thus explaining the high superheat. I'm glad the txv was non-adjustable so I wouldn't screw it up. Just reminded to ask questions before making assumptions. An explanation of operation laminated and mounted on the side of the unit would be perfect for future service calls cause I can see the next guy going through the same confusion I went through.