View Full Version : Compressor Burnout
onionhead
07-02-2006, 12:56 PM
Question Please
What causes compressor burnout, and how do you tell if that has occured?
Thanks
smokin68
07-02-2006, 01:21 PM
Alot of things. Acid in the system,excessive temps,factory faults,mis- wiring,low voltage,voltage spikes,etc.
You can tell when compressor doesn't run, and you open system up to acidic conditions(contaminated freon).
leapfrog
07-02-2006, 01:23 PM
Originally posted by onionhead
What causes compressor burnout Most common cause: incompetent installation, followed by poor service.
cmguy
07-02-2006, 03:00 PM
If the contactor at the compressor is energized but nothing is happening, no fan, no cold refrigerant to the coil, nothing, would this be compressor burnout?
leapfrog
07-02-2006, 03:02 PM
Probably not.
Sounds like it is time to call a professional.
cmguy
07-02-2006, 03:06 PM
Yes, I intend to. Air handler cfm increases as usual(York variable speed blower), but zilch at the compressor. As an electrician, after the contactor is energized and pulled in, that is where I make the handoff to you HVAC guys!
mjk_na
07-02-2006, 07:16 PM
Originally posted by onionhead
What causes compressor burnout, and how do you tell if that has occured?
In most cases, high temperature, FOLLOWED BY acid formation.
How can you tell? If the compressor refuses to start, check for acidity.
http://www.air-conditioner-selection.com/air-conditioning-maintenance.html
RoBoTeq
07-02-2006, 07:58 PM
The term "burnout" is used way too much in our industry for referring to simply failed compressors. A true burnout condition is quite easily identified by the acrid odor of the refrigerant oil and the acidity of that oil as well as the discoloration.
Without an oil sample, there is no way to determine if the compressor is a burnout.
hiltontech
07-02-2006, 08:43 PM
Originally posted by RoBoTeq
The term "burnout" is used way too much in our industry for referring to simply failed compressors. A true burnout condition is quite easily identified by the acrid odor of the refrigerant oil and the acidity of that oil as well as the discoloration.
Without an oil sample, there is no way to determine if the compressor is a burnout.
I totally agree.
star882
07-02-2006, 11:45 PM
Originally posted by RoBoTeq
Without an oil sample, there is no way to determine if the compressor is a burnout.
Sure there is. Disconnect the wires to the compressor and measure it with a multimeter. It won't be able to tell if it's an actual burnout, but it can tell if it's bad.
mjk_na
07-03-2006, 09:06 AM
Originally posted by star882
Originally posted by RoBoTeq
Without an oil sample, there is no way to determine if the compressor is a burnout.
Sure there is. Disconnect the wires to the compressor and measure it with a multimeter. It won't be able to tell if it's an actual burnout, but it can tell if it's bad.
Interesting. What should be the estimated reading be? Maybe I can learn something new :). Let's hope that this is not DIY.
star882
07-03-2006, 09:20 AM
Originally posted by mjk_na
Originally posted by star882
Originally posted by RoBoTeq
Without an oil sample, there is no way to determine if the compressor is a burnout.
Sure there is. Disconnect the wires to the compressor and measure it with a multimeter. It won't be able to tell if it's an actual burnout, but it can tell if it's bad.
Interesting. What should be the estimated reading be? Maybe I can learn something new :). Let's hope that this is not DIY.
Pretty simple. A (less than infinite) reading from any terminal to ground is bad. Then check winding resistance to make sure it matches up to datasheet specifications. It won't be able to tell if a turn or two is shorted, but that's when more sophisticated test equipment comes into play.
leapfrog
07-03-2006, 09:21 AM
I would hope that posting a link to public information otherwise available by a simple search would not be a violation of the Forum rules.
http://www.inspect-ny.com/aircond/aircond15.htm#aircond1D3
RoBoTeq
07-03-2006, 10:28 AM
Originally posted by star882
Originally posted by mjk_na
Originally posted by star882
Originally posted by RoBoTeq
Without an oil sample, there is no way to determine if the compressor is a burnout.
Sure there is. Disconnect the wires to the compressor and measure it with a multimeter. It won't be able to tell if it's an actual burnout, but it can tell if it's bad.
Interesting. What should be the estimated reading be? Maybe I can learn something new :). Let's hope that this is not DIY.
Pretty simple. A (less than infinite) reading from any terminal to ground is bad. Then check winding resistance to make sure it matches up to datasheet specifications. It won't be able to tell if a turn or two is shorted, but that's when more sophisticated test equipment comes into play.
I hope you don't mind if I don't take your comments seriously. First you dispute me with a statement that agrees with what I stated, then you post testing examples that are just wrong.