View Full Version : Condensation/moisture around condenser unit
cdonner
06-19-2006, 09:46 PM
Today I noticed a lot of moisture around one of the condenser units outside my home. The other one showed a lot less (but also ran for a shorter time prior to this). Is this expected? I don't remember ever noticing any condensation at my old house. Here, the water is literally running off the foundation of the unit.
The water does not come out of the condensation line from the unit in the house - that's at another location, and it is not quite as wet there.
alexb
06-19-2006, 10:39 PM
I could look down inside my Carrier unit,and the top half of the compressor would be sweating - but that's normal; the suction line feeds into one side, which makes it colder [than the dewpoint] outside, thus the condensation.
star882
06-19-2006, 10:48 PM
Some water is fine. Frost (looks like snow) is not.
billva
06-19-2006, 11:13 PM
Originally posted by cdonner
Today Here, the water is literally running off the foundation of the unit.
that is not right. when did you last have this looked at?
water "literally running" is not normal. some dripping, sure.
may be a good time to have it looked at and serviced for maximum efficiency.
mark beiser
06-19-2006, 11:15 PM
It could be normal, or it could be an indication of other problems.
When was the last time you had your systems checked? It would probably be a good idea to get them check out, and not by one of those "1 million point service check for $39" ripoff companies.
mjk_na
06-20-2006, 09:45 AM
Where is the exact location (on the condenser itself) of the water dripping?
I noticed the same thing my goodman condenser unit, not a lot of water but visable water around the unit. This was just installed.
any advice
excessive water is 1 of several things , dirty filter or evap coil or both, over charged system, dirty outside condensor , low air flow , make sure a vent are open . Call a good TECH
firecontrol
06-20-2006, 09:12 PM
Condensation/water at the outside unit is normal when it's humid outside. This condensation should stop at the compressor entry point. Any amount more than this is an indication of what was said above about low air flow problems or an overcharged system. Get it checked out before you loose the compressor due to damage.
cdonner
06-20-2006, 10:52 PM
The house is less than a year old and still under the builder's warranty. I am having the installer come to fix another more urgent problem (see http://hvac-talk.com/vbb/showthread.php?threadid=107955) and I will ask them about this as well.
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.