PDA

View Full Version : orifice size



melo
06-19-2006, 09:42 PM
I am replacing an existing 5 ton a/c system with a Trane 5 ton condenser and Armstrong 5 ton evaporator coil. the Trane specs list an orifice of .095. The evaporator coil specs list a .099 orifice. Is this an acceptable match or do I need to replace one and if so which do I change?
Thanks.

newoldtech
06-19-2006, 09:49 PM
You always go by the outdoor units requirements. As long as you know your dealing with a matched system.

melo
06-19-2006, 09:52 PM
Thanks for the quick reply... so to confirm, is the difference between the .095 and .099 enough to warrant changing the inside orifice to a .095 to match the outside unit?

billva
06-19-2006, 09:53 PM
it will not matter. why the strange combo?

melo
06-19-2006, 09:59 PM
I guess I can leave them alone - thanks.
reason is that I had to locate a 5 ton coil that would match the space requirements of the existing coil. The Armstrong was a good match for my existing Lennox coil (maybe because the Armstrong is a Lennox?). I also happened to come across the Trane condenser unit from a builder friend.....The two appear to be a good match seer and tonnage. But I noticed the slight discrepency in the orifice size.
Thanks!

billva
06-19-2006, 10:01 PM
there is no seer rating on that combo. so as far as you know, you may have an 8 seer.

melo
06-19-2006, 10:03 PM
BillVA,
so even though both have a seer of 13 the combo doesn't necessarily maintain that seer?

billva
06-19-2006, 10:06 PM
umm............

no.

melo
06-19-2006, 10:08 PM
what other specs should I be comparing to determine if this is a good match?

billva
06-19-2006, 10:09 PM
but the good news is, since it has never been tested, it may be a 19 seer. maybe you are on to something.

billva
06-19-2006, 10:11 PM
http://www.aridirectory.org/index.html

melo
06-19-2006, 10:12 PM
doubtful....but I will be happy if it works and is reasonably efficient...I will probably never know what the efficiency is. are there any other specs I should be checking to make sure they are a decent match?

vlux
06-19-2006, 10:47 PM
none of my business but orifice size is critical, like newoldtech said go with spec on outside unit, .095-.099 are differant will it be ok to use .099? Also dont understand your fits better problem, dont you get the best combo and do the plenum or ahu to match, sounds like you may not be taking the easy way if you end up with orifice problems jmo

billva
06-19-2006, 11:16 PM
Originally posted by melo
doubtful....but I will be happy if it works and is reasonably efficient...I will probably never know what the efficiency is. are there any other specs I should be checking to make sure they are a decent match?

nope. will not matter.

mark beiser
06-19-2006, 11:18 PM
Go with the #95 piston the outdoor unit shows.

Better yet, go with a TXV...